5-wire distribution system
I need to change the number of wires under Electrical Settings > Distribution systems. Current options are 3 or 4 wires for three-phase. Revit cannot create a 5-wire distribution system, the fifth wire representing a dedicated neutral wire. I need 5 wires where 3 wires are the phases, 1 wire is grounding and 1 wire is neutral.
8 Comments
Term "ground" is not quite clear. There are more options: - protective grounding conductor - functional earthing/grounding conductor - protective earthing/grounding and functional earthing/grounding conductor conductor - protective earthing/grounding and functional bonding conductor ... (see IEC 60050-195)
pavel.homan
I have chcecked the terminology according to the IEC 60050-195. I need to create 5-wire distribution system in Revit > solidly grounded neutral system - TN-S - where S is defined by “Separated” which means that the neutral and PE conductors are separated > three phases (L1, L2, L3), protective conductor (PE) - term by IEC 60050-195 and neutral conductor (N).
Scott_D_
See UK standard BS7671.
Equipotential Bonding conductor
PEN conductor - Protective earth and neutral
CPC - Circuit protective conductor
TNS - Earth and Neutral Separate
TNCS - Earth and Neutral Combined & Separate
SELV - Separated extra-low voltage
PELV - Protected extra-low voltage
ELV - Extra low voltage
LV - Low voltage
MV - Medium voltage
HV - High voltage
MET - Main Earth Terminal
Ring circuits
Circuits that measure along a containment system rather than as the crow flies
Lightning protection systems
Surge protection systems
High integrity earthing
Clean earth conductors
IT, TT, earth nests, LV and HV Earthing across transformers etc......
Martin__Schmid
Status changed to: Gathering Support
@pavel.homan - what would adding an option for '5 wires' enable you to do?  Presently, if you circuit a 3-phase piece of equipment, you, in fact, do have 5 wires as you described.. 3 phase, one neutral, and one ground.
Martin__Schmid
Closing this as implemented, as the desired outcome of "I need 5 wires where 3 wires are the phases, 1 wire is grounding and 1 wire is neutral." is possible in the software already.  Please feel free to add additional information or clarification if there are other previously unmentioned requirements or goals.
jbouchardFVVTL
I hate to resurrect an old thread. I've come across this problem when searching for a way to implement dual neutral distribution systems. Some of my clients require 200% neutral bars for their panels hence 2 neutral wires are needed. So if I count the ground wire, I'd end up with 6 wires in total.
Unless I modify my panel schedules to make the 'Wires' field manually set, I don't see a way to have this information readily available within the model.
Tarek_K
Tarek_K