I am trying to create a system where condenser water flows from a main pain to 10 different Water SOurce Heat Pumps. I have the correct flow through the main but when I assign a flow to the WSHP the flow goes back to the main and just adds it to the mains flow instead of subtracting it. For example, the main has 330 GPM and when i have a WSHP run off it at 5 GPM, the main after the WSHP reads 335 GPM instead of 325. Is there a way to fix it so that the WSHP are taking the flow instead of adding flow. 

 

Thank you

 

Mike

0 Likes
Reply
Accepted solutions (1)
372 Views
1 Reply
Reply (1)

nathan.chapman
Collaborator
Collaborator
Accepted solution

mdanaG5TSX-

Make sure whatever equipment these branch lines are serving has its connector set to in.  It hard to tell without seeing your file but it looks as though the branches are being told to push GPM back onto the system.  If there is nothing on the branches it might have to have some sort of family on it to force the system to subtract at each branch.

 