[RSA 2023] ACI 318 Moment Amplification Factor Incorrect
3 REPLIES 3
DonBAE
224 Views, 3 Replies
Per ACI equation 6.6.4.5.2 delta should be greater than or equal to 1.0, Robot currently allows values less than 1 to be considered.
Also when choosing "save project as"  with the Column-note tab active Robot attempts to save the model as a text document.
3 REPLIES 3
DonBAE
in reply to: DonBAE
the Beta,dns factor is also incorrect it should be calculated base on the ratio of dead load to total factored load.
DonBAE
in reply to: DonBAE
What is the beta factor in the load input, the help file does not define what this is used for:
okapawal
in reply to: DonBAE
This issue has been corrected in Robot Structural Analysis 2024 release. Release notes
Implemented condition for min delta for ACI318-14 & ACI318-19 according to p.6.6.4.5.2
Waldemar Okapa
Sr Product Owner
Technology Administrators