Hi @EY23
-why the Ix and Wx are not calculated?
These values are not calculated for the composite sections. You can enter them using the Section Browser in the User Section database based on the results obtained for the concrete section of the same shape.
-G is defined for all types of concrete, why it isn't calculated in the section.
As the final section properties are weighted based on E of the composite section components assigning the corresponding G value is not possible. On the other hand its influence would be only visible if you include shear in the deformation which you usually don't for ribbed slab.
-for the same load Fz for the composite section is larger than the ordinary one the pictures shows
As the composite beam is more rigid than the 'standard' one it 'attracts' more load from the slab. Compare the deflection of both beams.
If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.

Artur Kosakowski