I'm currently using Revit Light 2021 and I'm struggling with wall openings.
I have two wall openings at ground floor level that should go to the underside of beams - approximate height 1900 above floor level. However, when I have created the wall openings at GF level with an unconnected height of 1900mm, the opening continues up to the roof. This means that the ground floor opening is also visible at first floor. When I set the opening height to 600mm, it works as it should, but this is not at all useful for my plan drawings.
This occurs when I do new openings, or adjust the existing. I've attached a couple of screen shots to demonstrate. (I also note that the blue zone of the opening I'm showing appears to be wider than the (correct) visible opening).
Could someone assist me - is this because the wall I am cutting the opening in is attached to the roof? Is there a model setting that I'm overlooking? Have I got a strange quirk in my model!?
Solved! Go to Solution.
Solved by KarenLBR. Go to Solution.
Solved by KarenLBR. Go to Solution.
Solved by ToanDN. Go to Solution.
Ooooh, good spot! The wall is 2000 unconnected height.
When I change the unconnected height to 4000, the opening corrects itself.
Thank you!
Ooooh, good spot! The wall unconnected height is 2000mm.
When I change the wall to 4000 the opening corrects itself.
Thank you!