So I am having this major issue with the way Revit is deciding to do rounding for our Exiting Component Door Tags. For a sprinklered building, the means of egress capacity factor is 0.15. When I put 0.15 into a Revit formula it changes the number to 19/128 which is 0.1484375. This creates incorrect calculations at times and I can't seem to get the number to round up and/or I can't figure out a different fraction that won't increase the number drastically. Has anyone run into this issue and figured it out? We have a project that has 943 occupants exiting out of one door and the number is wrong. The required door width should be 141.45" and Revit is giving me 140". Even if we didn't need to round up or down, the number is still at least 1" off and that is concerning. Can anyone help? I have 2 families that I have attached. 1 is just a generic annotation and the other is a door tag. Both of them had the same formulas, but I tried to round up the generic annotation to see if anything worked.
Solved! Go to Solution.