After update thickness flange valve in SpecEditor.
The thickness of the valve flange are different in 3D model, same in specification !
The first length of port 1 is correct the second length of port 2 not same.
Result, bolt set are two lengths
Flange thickness is correct = 23.9
Only 1 thickness is changed with the update specification function ?
See attached file.
Best regards.
Solved by Bernd.Gerstenberger. Go to Solution.
Hi Serge,
when I look for your snapshot, I note that flange thickness 1 is 25.4 larger than for the second port: 0,9409 *25,4 = 23,9 (rounded). So, one port seems to be in inches, and the other one is in mm. Have you changed the units for one port in the catalog and afterwards you might have done a spec update from catalogs?
Best regards
Bernd
Hi Serge,
your screenshots aren't visible in the forum thread. We only see that: [cid:image001.png@01D537C3.7B671040]
Please, can you send me the spec and the catalog. Depending on the size you can just attach them to your email reply to my email or you can use the article to upload your data to the case.
Hi Serge,
sure. Therefore I have sent you a separate email. Just reply to this or upload it as described in the linked article.
Best regards
Bernd