Hello.
I’ve got some problem during calculating 2-storey building on seismic forces. I created modal case, but the “Rel.mas.UX(%)” and “Rel.mas.Uy(%)” are too low to add seismic case. I tried to increase number of modes up to 50, but I can’t even reach 70% to do residual mode as it was mentioned in one of the Autodesk presentation. I’ve added “Load to Mass Conversion” too, but “Rel.mas.UX(%)” and “Rel.mas.Uy(%)” isn’t rising anyway.
P.S. In RSA there isn’t my country’s seismic codes, so I’m trying to calculate model with the help of spectral method.
Can someone help me solving this problem?
There are some screenshots below.
Solved! Go to Solution.
Solved by Rafal.Gaweda. Go to Solution.
Hi @Anonymous
Without Active Mass Direction Z you need 8 modes.
Otherwise 226.
When I turned off Active Mass Direction Z, for all modes “Rel.mas.UZ(%)” =0 it worked (percentage is higher than 70%)
According to this, I have another question:
Is it reasonable to turn off Z direction, in this calculation?
Is it okay, that for main modes, such as 1; 2; and 3, “Rel.mas.UX(%)” and “Rel.mas.UY(%)” are lass than 70% ?
Hi @Anonymous
Is it reasonable to turn off Z direction, in this calculation?
NO, because you have very heavily loaded beams in case 2, so you can't neglect the vertical vibration of these beams.
Moreover, you already reach 90% of mass in mode 4 for Z.
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
@Anonymous
your structure is very steep in the first level.
If you consider that the other floors are embedded in the first level you already get 82% in X from mode 2
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Hi @Simau
Firstly, thank you for response.
Moreover, you already reach 90% of mass in mode 4 for Z
Is it enough, to continue calculation for seismic case, regardless masses for X and Y aren't reached 70% ?
Your structure is very steep in the first level.
The vertical reinforced wall (concrete plinth) in the first level is due to there are horizontal loads from ground. That's why it is steep.
If you consider that the other floors are embedded in the first level you already get 82% in X from mode 2
To be honest, i didn't understand what you mean, can you explain ?
Hi @Anonymous
I just wanted to point out that in very stiff structures at the bottom, the masses of these levels are mobilized only at very high frequencies, sometimes exceeding the cutoff frequency of 33Hz.
In this case a good opinion on the seismic behavior of the structure can be obtained by considering the flexible part of the built-in structure in the rigid part.
Looking at the mobilized masses in X and Y below 33 Hz, you are not so far from the 70%, so in my humble opinion you can use the residual mode.
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Just to complete my point of view, in the substructure model we see that the mobilized mass is 82% at mode 2.
So in the complete model you are sure to have mobilized all the mass of the upper part of the structure before 33Hz. This upper part being the sensitive part of the building.
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Firstly i'm relay interested, if it is necessary to have 60 or more modes for 2-story building?
Secondly, i can't find mobilized mass (82%) in mode 2, and which direction we're talking about? Can you show me where is it, please.
It'd be great if you advice me some manuals about this topic, so that i could read it.
Thank you in advance.
@Anonymous
Maybe I was not clear enough, sorry
Firstly i'm relay interested, if it is necessary to have 60 or more modes for 2-story building?
it is not a matter of number of modes, the goal is to know if the number of mode retained is sufficient to estimate the efforts in the part of the structure which interests you.
In this case, it is the upper part of your structure that is sensitive to earthquakes. In the model (sous-structure) of this part alone, you can see that mobilized mass is almost 100% in X and Y with only with 7 modes.
It would be good if you compare the efforts in some elements of the high part obtained with 7 modes in these models with and without the lower part.
Secondly, i can't find mobilized mass (82%) in mode 2, and which direction we're talking about? Can you show me where is it, please.
The 80% in mode 2 are related flexible structure only without the lower part, see attached file in post 7.
It'd be great if you advice me some manuals about this topic, so that i could read it.
see attached file (in French :0( )
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
sorry
first page was missing
here new doc
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Can't find what you're looking for? Ask the community or share your knowledge.