I have a multistory building which is for some reason getting unreasonably large forces on som shear walls.
For Wind-cases in Y-direction, one shear-wall which is oriented in X-direction is getting large shear-forces. The walls are free and is not supposed to work toghether. Is there a way to avoid this effect?
Solved! Go to Solution.
Solved by Simau. Go to Solution.
You want Axis B core wall to work for loads on X direction only and the the one on axis C only to work for loads on Y direction ??
What do you mean by "The walls are free" . Is the structure separated ( 2 pieces)?
Rafael Medeiros
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
The walls have linear-releases, and should not transfer moment or shear to each other.
It seems to me that panel number 29 has to large horizontal shear-forces. If you compare it to panel number 32 and 37. This seems a bit strange to me since the force is placed in Y-direction.
Could you share your model?
M. Agayr
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Nothing strange in the results.
The wind in the Y direction is applied to the center of garvite which is at x = 13.42m, the center of rigidity is at x=26.3m. The twist couple created is taken up by the shear walls in X direction.