Hi,
I'm trying to design a pad footing( 6.0x6.0x2.0m) according to EC7 - DA2.
The imposed loads are
DEAD LOADS:
600ΚΝ vertical load plus self weight of foundation automatically calculated by Robot(6.00x6.00x2.00x24.53=1766.16KN)
LIVE LOADS:
300KN horizontal load
3000kNm moment at the the top of footing.
The design combination for soil capacity is 1.00DL+1.50LL
In the calculation note it seems that the total vertical dead load is calculated with a partial factor 1.00 for the imposed dead load and with 1.35 for the self weight: Ν=1.35x1766.16+1.00x600=2984.32KN.
Is this calculation correct?
Also I would like to ask if it's possible to design according to DA2* (maybe by editting some. rgl file?)
Thank you.