Beam check/ Lateral restrain

Beam check/ Lateral restrain

simjack
Enthusiast Enthusiast
1,821 Views
3 Replies
Message 1 of 4

Beam check/ Lateral restrain

simjack
Enthusiast
Enthusiast

Hello,

 

I wanted to ask if there is a simple way to laterally restrain beams. At the moment I just applied restrains at every 0.05L however I am not sure whether that is the right procedure. 

 

In the attached model, I am only interested in the lower level portal frame. I performed a simple check to see whether the load is being distributed correctly. I applied a permanent load 2kN/m2 on the first floor slab and calculated a deflection for the middle beam (10) to be 16.5mm (5x(2x4.3)x7160^4)/(384x210000x8500x10^4). I understand it's two point loads rather than UDL however the difference is so large. Can you please advise why can this be?

 

Thank you. 

0 Likes
1,822 Views
3 Replies
Replies (3)
Message 2 of 4

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @simjack

 

I wanted to ask if there is a simple way to laterally restrain beams. At the moment I just applied restrains at every 0.05L however I am not sure whether that is the right procedure. 

 

This will work but you can also do this like that:

 

LTB restrain.PNG

 

In the attached model, I am only interested in the lower level portal frame. I performed a simple check to see whether the load is being distributed correctly. I applied a permanent load 2kN/m2 on the first floor slab and calculated a deflection for the middle beam (10) to be 16.5mm (5x(2x4.3)x7160^4)/(384x210000x8500x10^4). I understand it's two point loads rather than UDL however the difference is so large. Can you please advise why can this be?

 

IMHO you disregarded the fact that part of the load is taken by both the slab and perpendicular beams as they have their stiffness too.

 

 

If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.



Artur Kosakowski
0 Likes
Message 3 of 4

simjack
Enthusiast
Enthusiast

Hello,

 

Thank you for your answer. 

 

 

IMHO you disregarded the fact that part of the load is taken by both the slab and perpendicular beams as they have their stiffness too.

 

 

 

Are you implying that in the model the stiffness of the slab gives it the ability to spans between outer beams? In reality the slab would be supported on the intermediate beams with simple pin connections so the vertical load should be taken by the beam 10 and the corresponding perpendicular beams. Is there a way how to correct this?

 

Thank you.

0 Likes
Message 4 of 4

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @simjack

 

Are you implying that in the model the stiffness of the slab gives it the ability to spans between outer beams? 

 

If you define it at the beam lecvel and mesh then it is what actually happens.

 

In reality the slab would be supported on the intermediate beams with simple pin connections so the vertical load should be taken by the beam 10 and the corresponding perpendicular beams. Is there a way how to correct this?

 

Assuming you don't need to check the results for the slab itself you can do it in this way:

 

panel calculation model4.PNG 

 

Otherwise mesh the panel but define it above the beams and connect it with the beams with short bar elements (pins).

 

If one or more of these posts answered your question, please click Accept as Solution on the posts that helped you so others in the community can find them easily.

 