Hello,

 

I've looked around quite a bit and couldn't find any information on this, so any help or direction would be appriciated.

 

We have a distribution panel that is defined as a switchboard. The panel schedule works as needed EXCEPT we are unable to move any 2-pole circuits to the B/C phases. Is this just a limitation (I'm thinking yes), or is there some fancy way to get the loads to move over?

 

We tried the Panelboard/1-column schedule idea, but in the end the circuits are listing as 1,2,3 and we would like them listed as they would with a switchboard panel (showing 1 number per circuit, regardless of poles).

 

Any thoughts? What have others been doing?

 

We are running in Revit 2015 currently.

 

Thanks!

Casey

Reply
7,035 Views
9 Replies
Replies (9)

fabiosato
Mentor
Mentor

Hello,

 

I have found out that switchboard fits to 3phase loads, 2 phase and 1 phase will use from phase A, so 2 phase (AB) and 1 phase (A).

You can try to make loads 3 phase unbalanced and place values to phases B and C. I didn´t tried it.

Fábio Sato
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

Anonymous
Not applicable

Sorry to comment on an old thread, but this is a problem that still exists on Revit 2017.

See my screenshot for an example.

Capture.PNG

 

Has anyone here found a fix?  I think fabiosato's workaround should work, but it's a painful workaround to use on numerous circuits.

 

Thanks,

Ryan

0 Likes

Anonymous
Not applicable

Disconnect your 2-pole loads from the SB, place a 1 pole spare in the schedule, and reconnect the loads.

Anonymous
Not applicable

Fabiosato's idea sorta worked. Smiley Indifferent

BSammis' idea didn't. Smiley Sad

Capture2.PNG

 

0 Likes

Anonymous
Not applicable

It works if you change your DB family part type from "switchboard" to "panelboard" and use a modified single column panel schedule.  Which is also how we get around the disconnect between lines in the schedule and total number of 1 pole breaker spaces in the panel.

0 Likes

Anonymous
Not applicable

Capture3.PNG

 

bsammis,

Thanks.  That works pretty well, and I'm satisfied enough to use this method going forward.  However, I don't love the numbering.  As casquatch said in the OP, we want the circuit numbers to be 1 digit, like a switchboard.  Do you have a fix for that?

0 Likes

scbunker
Collaborator
Collaborator

Anybody have an answer for this?

0 Likes

scbunker
Collaborator
Collaborator

I've created an Idea for this. It is important that we have this functionality in the software.

 

https://forums.autodesk.com/t5/revit-ideas/allow-selection-of-phases-in-switchboards/idi-p/7381023

 

Please go vote for it and maybe we'll see it happen!

0 Likes

Martin__Schmid
Autodesk
Autodesk

A solution to this was implemented in Revit 2021.  See this help topic.



Martin Schmid
Product Line Manager
Mechanical Detailing and Electrical Design