Pipe flow calculation by creating shared/Project parameters in roof drain

dipen609
Contributor
Contributor

I have modified the roof drain family and assign the area and rainfall to calculation flow(GPM) . The family works fine but when I connect the pipe to the family the flow is not reflected on pipe. Please refer the attached file.

 

Thank you, 

0 Likes
Accepted solutions (1)
2,464 Views
10 Replies
Replies (10)
Message 2 of 11

iainsavage
Mentor
Mentor

It would be best to upload your family for testing.

The pipe connector should be set to Preset, Out and Sanitary.

Its flow value should then be associated to your flow parameter.

Your pipe system in the project would also be Sanitary classification for roof drainage.

 

 

0 Likes
Message 3 of 11

dipen609
Contributor
Contributor

Hi, Thanks for you time. I am trying to assign parameter and use hydronic return piping to calculate flow, the flow shows in the roof drain but not in the connected pipe. I have attached the project file and family file. Please refer the video ( 6:20-9:21) This is what I am trying.  Thank you.

 

https://www.autodesk.com/autodesk-university/class/Automating-Plumbing-Design-Revit-2016#video

0 Likes
Message 4 of 11

iainsavage
Mentor
Mentor

Its the Hydronic Return classification which seems to be causing the issue.

When I change it to sanitary it looks for fixture units (even though the connector is set to Preset rather than Fixture Unit).

Domestic Cold Water works though.

PS: did you mean to have two outlets in the family, one of which doesn't have a connector?

iainsavage_0-1631082413486.png

 

0 Likes
Message 5 of 11

dipen609
Contributor
Contributor

Thank you, 

The intent of using hydronic return is that I want to size the roof drain pipe based on GPM(flow) not the Fixture Units(FU). I understand it works fine when we use sanitary system. 

 

What I am trying to do is tested by someone. Please refer webinar in below link. Can you please have a look from 6 minutes to 9 minutes. 

 

https://www.autodesk.com/autodesk-university/class/Automating-Plumbing-Design-Revit-2016#video

0 Likes
Message 6 of 11

iainsavage
Mentor
Mentor
Accepted solution

I've seen that video before but had never tried it for real.

All that I can tell you is that it doesn't work with Hydronic Return in your project or in my test project. 

System Inspector shows confusion over flow direction and zero flow in all pipes.

iainsavage_0-1631165870714.png

With the classification changed to Domestic Cold Water it works correctly and reports flow values, not fixture units.

iainsavage_1-1631166250177.png

(Preset = constant flow not fixture units. Fixture units are only activated with the Fixture Unit option)

iainsavage_3-1631167032927.png

 

The other option that I tried was to leave the system as Hydronic Return but changed the floor drain family to Mechanical Equipment and that also works:

iainsavage_2-1631166607831.png

 

Maybe, given the age of that video, there has been a change in the software and now maybe "mechanical" pipe systems aren't compatible with plumbing systems?

So my recommendation is change your connector to Domestic Cold Water, Preset, Out. 

 

Note that these "flow" values are actually the catchment areas of the drains because you haven't put in the formula for sqft to gpm yet. 

0 Likes
Message 7 of 11

dipen609
Contributor
Contributor

Thank you for your time. Yes, it works with Domestic cold water system.

0 Likes
Message 8 of 11

cbeliveau5TAHS
Observer
Observer

Link the flow parameter to the connector and that should solve the issue. 

0 Likes
Message 9 of 11

iainsavage
Mentor
Mentor

@cbeliveau5TAHS wrote:

Link the flow parameter to the connector and that should solve the issue. 


That wasn’t the issue. It was the system category which was incompatible with plumbing fixture family per the marked solution - just for any future readers.

0 Likes
Message 10 of 11

cbeliveau5TAHS
Observer
Observer

I have a similar setup using hydronic and worked. I'm curious what was not compatible. 

0 Likes
Message 11 of 11

iainsavage
Mentor
Mentor

Parts 4 and 6 explain it.

The flow parameter was associated with the connector, obviously, but with the OP’s choice of Hydronic Return and Plumbing Fixture the flow did not transfer into the pipes.

The video which they posted the link to did work with that combination and on that basis I suspect that this behaviour might be version-dependant.

The issue was solved by using Domestic Cold Water instead of Hydronic Return.

If you have it working as the OP originally wanted then please explain how, or share a copy of your model.

0 Likes