Panelboard Total Load on Phase B is not adding up correctly

Panelboard Total Load on Phase B is not adding up correctly

Anonymous
Not applicable
727 Views
2 Replies
Message 1 of 3

Panelboard Total Load on Phase B is not adding up correctly

Anonymous
Not applicable

I am using J-boxes to make Existing loads for a panel schedule, Phase A and C are fine and total correctly but Phase B has 2 J-boxes both with 1680VA and a Lighting circuit with a load of 2132VA this circuit has 2x4s, downlights, etc.. the total load should be 5492VA but the load is in at 5430VA and I can't figure out the issue. I deleted the J boxes and the total was 2132VA like it should be so it seems the issue is with the J boxes but neither of the other phases is having this issue and they are comprised on only J box loads.

0 Likes
Accepted solutions (1)
728 Views
2 Replies
Replies (2)
Message 2 of 3

fabiosato
Mentor
Mentor

Hello,

 

Did you check if the power factor of all loads are set to 1? The default sum method for the power is a vector sum.

Fábio Sato
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 3 of 3

Anonymous
Not applicable
Accepted solution

Under the Manage tab I went to MEP Settings > Electrical Settings. I changed my Load Calculations settings to Sum apparent load. Everything is adding up straight forward