Hello everyone !

I need help in solving this error message :

 

"SA 1583: It is not possible to calculate the flow since there is inline equipment that is configured as end of line. Please check equipment in this system and make sure that the equipment connectors used inline have a global system classification and a calculated flow configuration. Global equipment connectors used inline should always be linked to each other."

 

(I'm Trying to produce a pressure drop report for the ductwork)

 

 

0 Likes
1,026 Views
8 Replies
Replies (8)
Message 2 of 9

RobDraw
Mentor
Mentor

That message describes what Revit needs in order to do the analysis, pretty clearly. 

 

Have you checked all your inline equipment? (I've seen VAVs incorrectly categorized as air terminals.)


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.
0 Likes
Message 3 of 9

YoavG88H3Z
Explorer
Explorer

I got only diffuser and dampers installed on duct-work connected to AHU...

no vav's...

0 Likes
Message 4 of 9

RobDraw
Mentor
Mentor

Have verified that the families are setup correctly?


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.
0 Likes
Message 5 of 9

YoavG88H3Z
Explorer
Explorer

What do you mean by saying correctly?

0 Likes
Message 6 of 9

RobDraw
Mentor
Mentor

Try the stuff in the message?


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.
Message 7 of 9

YoavG88H3Z
Explorer
Explorer

YES, I have been tried to change it to global connector but still I got that error.

0 Likes
Message 8 of 9

RobDraw
Mentor
Mentor

Did you address the FIRST sentence in the error message?


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.
0 Likes
Message 9 of 9

iainsavage
Mentor
Mentor

Make sure the damper is a Duct Accessory.

Part Type "Damper".

iainsavage_0-1689521456402.png

 

Make both connectors Global.

Set them as bidirectional.

Set their flow configuration as Calculated.

Link the connectors.

iainsavage_1-1689521532365.png

 