Having multiple connectors to an air terminal,unable to compute pressure drop

Having multiple connectors to an air terminal,unable to compute pressure drop

Anonymous
Not applicable
583 Views
2 Replies
Message 1 of 3

Having multiple connectors to an air terminal,unable to compute pressure drop

Anonymous
Not applicable

Hello, I made a slot diffuser with array connectors (multiple connectors) it perfectly worked, but during pressure drop calculations, if more than one connection is set , the Revit shows a message "not computed" Can any one have a solution.  

0 Likes
584 Views
2 Replies
Replies (2)
Message 2 of 3

mhidshaji
Participant
Participant

Make separate diffuser for each connector portion of a slot diffuser.

 

slot.PNG

Message 3 of 3

marco.defina
Collaborator
Collaborator

Hello,

 

ihave the same issue and Autodesk opened a case after my report:

 

https://knowledge.autodesk.com/support/revit-products/troubleshooting/caas/sfdcarticles/sfdcarticles...

 


The Development Team will try to make an initial assessment. The fix requires the code for Revit to be modified, and as such, we do not have a timeline for when any fix may be released. 


 

 

The solution of @mhidshaji is the only solution at the moment.

 

 

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________