@HVAC-Novice Please see responses from my engineer:
What type of system is it? 240V 3-Phase High Leg Delta
Is it 240V between legs, or from leg to neutral? This is fun, 3-Phase High Leg has a 240 leg to leg. The A leg and the C leg are 120 V from leg to neutral, the B leg is 208V from leg to neutral.
Do you mean the European 230/400V system? No, see above.
What device would only use 2 phases? The distribution panelboard feeding the panel we are working on is 1 Phase (2 legs) 240/120V. To not have the B leg going to the panelboard, this would create a 208V leg to neutral which is not something most equipment is rated for, a three-pole breaker is connected to the panelboard because the buss goes A>B>C>A>B>C… as you go down the circuits on a panelboard. This means that to get only the A and C phases, you would have to pick a specific breaker number like 5,7 to get a situation where it is C>A between two poles in sequence.
Why a single-phase panel with a family that seems to use 3 poles? Answered above
Why a 3-pole breaker on a 2-pole device? To avoid the B leg, a three-pole breaker is attached but no conductors are connected to the B leg only the A and C, neutral and ground.