chilled water flow and system

chilled water flow and system

SumanrajS4YXL
Explorer Explorer
139 Views
2 Replies
Message 1 of 3

chilled water flow and system

SumanrajS4YXL
Explorer
Explorer

Hi, I am currently working on a chilled water plan. I have completed one floor and then synced the project. However, after syncing, some of the chilled water pipe tags are displaying question marks instead of the flow rate. How can I resolve this issue?

chiller water.png

 

0 Likes
Accepted solutions (1)
140 Views
2 Replies
Replies (2)
Message 2 of 3

iainsavage
Mentor
Mentor
Accepted solution

This would tend to indicate that there are errors (e.g. disconnections, incorrect connector settings, cross-connections between different systems etc) in your piping network.

You should be able to use the "Check Pipe Systems" and "Show Disconnects" tools and click on the warning triangles to see what the error messages are.

0 Likes
Message 3 of 3

navya_gelli
Autodesk
Autodesk

Hello @SumanrajS4YXL,

 

Just checking whether your issue has been resolved and if iainsavage response answered your question. If you're still experiencing issues, please comment below so the community can help. If you've resolved the issue, please let us know what worked for you.

 

Navya | Community Manager
0 Likes