Unfortunately, it's not as simple as changing the system type from the properties. If you have equipment such as diffusers or FCU's attached then they will have connectors on them set to a system classification which should match the classification of the system you have connected to them (ie Return Air). If they are different then you would have got a warning about it as it will have been a mismatch. To change your system then you will 1st need to physically disconnect all of the air terminals and mech equipment from your system (anything with a defined system classification). Then you will need to edit duct system and remove all of the disconnected stuff from system, exit out of the editor. You will then be able to select a single piece of duct and change the system type from Exhaust Air to Return Air. You will also have to edit or swap your families out for ones with connectors to match the classification of your required system. Not a quick fix if it is a large system I'm afraid.
I hope this helps you out.