Automatic pipe sizing errors

merhef.asc
Explorer
Explorer

Hi,

when, automatically,  sizing a water supply piping system with water heater in, always generate error. once the water heater is removed all are fine. any one can help

0 Likes
Accepted solutions (1)
380 Views
5 Replies
Replies (5)
Message 2 of 6

tim.ingle
Enthusiast
Enthusiast

Hi @merhef.asc, can you share the Water Heater family that you are working with? I believe something might be calculating incorrectly from the piping connector(s) within the Water Heater family.

0 Likes
Message 3 of 6

merhef.asc
Explorer
Explorer

thank you for the follow up,

 

it is out of the box Revit family, I have tried more than one family  but same issue. here it is. 

 

regards 

0 Likes
Message 4 of 6

Nathan.HilsonN67V6
Advocate
Advocate

Can you post a quick screencast of what it's doing? Also, what content are you drawing with, Generic revit families, Revit fab parts, or a custom content pack such as building data? 

0 Likes
Message 5 of 6

iainsavage
Mentor
Mentor
Accepted solution

Edit the water heater family as follows:-

  • Create an instance flow parameter for hot water and assign it to the hot water outlet connector.
  • Create an instance flow parameter for cold water and assign it to the cold inlet connector.
  • For the cold water flow parameter insert a formula to make it equal the hot water flow parameter.

Reload the family into your project.

Flow should now pass through the water heater with the correct values.

0 Likes
Message 6 of 6

merhef.asc
Explorer
Explorer

thank you, it works 

 