- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report
My Nonlinear Transient Heat Transfer analysis is yielding unreasonable results. To troubleshoot, I have created a simple model and ran a Nonlinear Steady State Heat Transfer analysis. The problem appears to be a failure to interpolate the convection coefficient from a temperature-convection data table. I'd like someone to review my findings and help me achieve the desired behaviour. I'm using Autodesk Inventor Nastran Version 2023.3.0.67.
The simple model is a solid block with near perfect thermal conductivity. I have a temperature load on one face and a convection load on the opposite face. This way, I can effectively choose the uniform temperature of the convection surface, which allows me to verify that the correct convection value was interpolated from the table.
The temperature in the simulation is ~392 K, which should result in a convection coefficient of 15 671.1 W/(m^2 K). With an Ambient Temperature of 313 K, I should get a flux of (392 K - 313 K) * (15 671.1 W/(m^2 K)) = 1.238E+6 W/m^2.
However, the simulation results show 2.607E+5 W/m^2. That would require a convection coefficient of 3300 W/(m^2 K). Something is not right.
Now, if I copy and paste the convection coefficient for 392 K from the table into the load definition as a static value and re-run the simulation, I get a heat flux of (392 K - 313 K) * (15 671.1 W/(m^2 K)) = 1.238E+6 W/m^2. That's correct!
I don't understand why Nastran cannot interpolate/select the correct value from the table. Thoughts?
-Adam
Solved! Go to Solution.