The blocks listed below will have issues, due to the filename. There is a drives table (DR) so the Powerflex should be named something like HDR1_PF525.dwg if the wires are connected horizontally. Use a "V" for the first letter of components that are wired vertically. If you have mostly horizontal wire connections but a few vertical as well, use "H" for the first letter. The underscore precedes an optional "unique identifier", in case there could be more than one variation of this device.
GRACE: Graceport Receptacle with Ethernet
This could be named HC01_ENET because the table for connectors is C0, and that is the letter C and number zero.
1492-XIM2024-16RF: 16 Point relay output module
PLC module filenames/block names are an exception and must begin with PLCIO, so they go to the proper table for part numbers and also it triggers a different version of the Insert/Edit Component dialog that allows for addressing, function text, etc. I prefer PLCIO_ followed by module number.
PF525: Powerflex 525 Drive (HDR1_PF525.dwg as explained in fist paragraph)
K300: Kinetix 300 and 500 Symbol (same rule as with the Powerflex, something like HDR1_K300)