Form-C contacts default and reverse

Form-C contacts default and reverse

Anonymous
Not applicable
3,069 Views
16 Replies
Message 1 of 17

Form-C contacts default and reverse

Anonymous
Not applicable

Good day all,

 

We are very happy with using ACADE for our railway interlocking system schematics, but so far we are creating new blocks and dynamic drawings between parrent coils and child contacts some troubles occour.

 

In base we have pinlist 3,11,12,13;3,21,22,23; ......... so no voltage on coil means NO is 11-12 and NC is 11-13.....

 

In our schematic logic is very common that if we have arrow (in our case in Description2 attribute) under parrent coil there is voltage on coil and we sign NO like 11-13 and NC 11-12 with arrow under contacts too.

 

I know this style of drawing electrical schematics is non-standard, but this is historicaly defined in our case. 

 

Is it possible to make some script or advanced settings to reach this automatically: "If arrow symbol in Description2 in parrent then increase Pin2 +1 in all NO child contacts, decrease Pin2 -1 in all NC child contacts and so in 3 terms NONC contacts too" It means still NO and NC contacts but visible value is +1 or -1.

 

And yet one question. I have NONC contact (Form-C) with 3 Terms. What number will be on fifth character in symbol naming for NONC? NO is 1 and NC is 2 but 3 terms NONC definition is what number? 

 

Thank you for answer.

0 Likes
Accepted solutions (2)
3,070 Views
16 Replies
Replies (16)
Message 2 of 17

dougmcalexander
Mentor
Mentor
Form-C contact symbol blocks are named HCR23 or VCR23. Symbols for these already exist in the IEC and NFPA library folders.

Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623

Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 3 of 17

rhesusminus
Mentor
Mentor
The number is 3.

And yes, I guess it would be possible to update whatever according to some rules you set.

Trond Hasse Lie
EPLAN Expert and ex-AutoCAD Electrical user.
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉
0 Likes
Message 4 of 17

Anonymous
Not applicable
Thank you, but what rules and where i have to set up? 🙂 I know its advanced topic however where can i read this kind of solution?
0 Likes
Message 5 of 17

dougmcalexander
Mentor
Mentor
Accepted solution
Use the Catalog Browser to edit the record for the part number of the relay. Look out to the right of the row for two fields, one for Coil Pins and the other for the Pin List. Click in the cell to get the menu for assigning pins, or you can type in - (i.e. 3,Common,NO,NC)

Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623

Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 6 of 17

Anonymous
Not applicable

Doug, thx for your answers. My last question is clear now. But what about the previous problem:

 

Is it possible to make some script or advanced settings to reach this automatically: "If arrow symbol in Description2 in parrent then increase Pin2 +1 in all NO child contacts, decrease Pin2 -1 in all NC child contacts and so in 3 terms NONC contacts too" It means still NO and NC contacts but visible value is +1 or -1.

0 Likes
Message 7 of 17

dougmcalexander
Mentor
Mentor
There is no built-in function for handling your request. There are options under Drawing Properties to show unused contacts, in case a 4PDT has extra contacts available.

Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623

Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 8 of 17

rhesusminus
Mentor
Mentor
Can you supply some more information? Maybe a picture or two of what you have before and what you want after a macro has run?

Trond Hasse Lie
EPLAN Expert and ex-AutoCAD Electrical user.
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉
0 Likes
Message 9 of 17

Anonymous
Not applicable

Yes I will post pictures tommorow....

 

Now I have another problem with pop-up: Alert - pin aasignment repeated.

 

When I copy child contact symbol HCR21 or HCR22 and place with same pins - Alert shows - its OK.

 

But when I copy child contact symbol HCR23 and place with same pins - no Alert shows.

 

Its very useful Alert but I dont know why it doesnt work for NONC contacts...

 

PS: What is differrent when I use attribute NONC or NCNO in symbol editor? There is NO, NC and NONC choice in default but concretely symbol HCR23 has attribute NCNO.

 

THX for your answers...

0 Likes
Message 10 of 17

Anonymous
Not applicable

OK I have picture about my problem...

Again here is description:

 

Is it possible to make some script or advanced settings to reach this automatically: "If arrow symbol in Description2 in parrent then increase Pin2 +1 in all NO child contacts, decrease Pin2 -1 in all NC child contacts and so in 3 terms NONC contacts too" It means still NO and NC contacts but visible value is +1 or -1.

 

And picture:

Figure1.png

0 Likes
Message 11 of 17

Icemanau
Mentor
Mentor
Accepted solution

There may be an easy way to do what you are after...

 

Edit the catalogue and copy the entire entry. Now modify the copy by changing the PIN LIST to show as if the coil is powered along with adding a ' POWERED' or similar to the catalogue number and stating the coil is shown powered in the description.

 

Now when you the catalogue number for the relay, you select the powered or unpowered version and the contacts should come in correctly without messing around with scripts, post processing or anything else like that.

 

Regards Brad

>

Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 12 of 17

Anonymous
Not applicable

Thank you, this is the way using catalogue with another pin list row. But its not so clear because there is two same component in catalogue anyway.

 

If anyone have Idea about some script, it would be fine 🙂

 

THX

0 Likes
Message 13 of 17

rhesusminus
Mentor
Mentor
This can be programmed, but unfortunately, I don't have time to do a freebie for a while.

Trond Hasse Lie
EPLAN Expert and ex-AutoCAD Electrical user.
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉
Message 14 of 17

Anonymous
Not applicable

Thank you,

 

I know its advanced issue and I agree with you 🙂

 

However is ther any chance to study this issue..any websites with autocad scripting?

0 Likes
Message 15 of 17

Anonymous
Not applicable

I tried the solution by Icemanau with UNPOWERED and POWERED pin lists.

 

Everything looks good, pins are distributed exactly from wanted pin list, but if I decide to change between unpowered and powered catalogue device, the Alert appears:

 

Figure2.png

 

It is very unpracticle surf every child contact and change their pins 😞

Do I something wrong? Or can be there other solution to reach this effectively?

 

Many thanks

0 Likes
Message 16 of 17

Icemanau
Mentor
Mentor

No, you did nothing wrong and there is nothing that can be done about the warning.

It comes up whenever you change the catalogue selection and is normal for ACADE.

 

As for surfing to find each contact, I posted this idea a while back about the Pin List...

https://forums.autodesk.com/t5/autocad-electrical-ideas/contact-pin-selection/idi-p/5610401

 

Regards Brad

>

Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 17 of 17

Anonymous
Not applicable

Rhesusminus...for awhile or forever? 😄

 

Is there any chance to discuss the solution with you? What would break a freebie in your case?