Ultimate shear resistance results interchanging two different values for Vc/Vco
Hi there,
I'm carrying out an grillage analysis of a prestressed concrete beam bridge with infill concrete between/above the webs (see pic one).
Vco =  130.014, yet in the next section as the cracking moment is greater than applied, Vc=Vco but then Vc is stated as =133.937 (see pic two)
I've attached the results file, not sure what is going on so would appreciate any help you can offer.
Charlie
karoly_tarcsi
Hi Charlie,
Can you zip and attach your model for inspection?
Karoly Tarcsi
Software Development
(If you are satisfied with the answer, can you "Accept Solution ", so others can learn from it. Thanks.)
Karoly Tarcsi
Here you go
karoly_tarcsi
Hi Charlie,
In Clause 6.3.4.2 shear capacity of "PC-beam only" is calculated as 130.009kN.
However capacity of composite section in Clause 7.4.2.2 is found to be 133.937kN after the evaluation of shear strength of the infill in Clause 5.3.3, resulting Vc = 133.937kN in Clause 6.3.4.2.
Please find attached a marked-up shear design report of your Inner beam SB1.
Karoly Tarcsi
Karoly Tarcsi