Unsatisfactory Load Capacity of the Column
Μηχανικος
Message 1 of 14
Μηχανικος
I am designing a 2-storey RC Frame house and most of the columns get the error "Unsatisfactory Load Capacity of the Column" when designing the reinforcement.
one of the columns is 600x250mm, after the error I tried to increase the size of the column (within the provided reinforcement module) to 600x600mm and again i get the same error. ( i did not recalculate the analysis)
i even increased the column to 800x800mm and again i get the same error.
I also tried 900x900mm  and it worked, well i have never seen such a column in a house or even a 5 storey RC frame so something is certainly wrong here.
can someone help me?
below is the design that actually worked..... excessive you say???
The column highlighted is the one being designed no.5
 Diagrams below are shown for both the column being designed and the column above
Loadcase: Code combinations
This is the shear force on the column on the Z direction FZ
This is the shear force on the column on the Y direction FY
This is the axial force FX
This is the Bending Moment MY
This is the Bending Moment MZ
Replies (13)
Message 2 of 14
Μηχανικος
I tried increasing the dimensions of the column only on one side to 900x250mm and now it works.
i will try the same with all columns and see the end result.
Message 3 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Μηχανικος
My understanding is that you expect the column to be of a smaller size. If so, from my experience usually the issue is not with the RC Design but with the values of internal forces you get for a column. Are they as you expect them to be or larger? Perhaps you should look at the value of the base shear for seismic analysis and compare it to the static force procedure (assuming you defined the response spectra one) or change the supports from fixed to pinned.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
Message 4 of 14
Μηχανικος
Instead of changing the support from fixed to pinned dont you think its better to just decrease the stiffness of the fixed support, lets say for example to 80% of the current stiffness.
But you are right though, in real life the supports even in RC frames are never fully fixed.
Message 5 of 14
Μηχανικος
I will check the base shear of the design response spectrum against the equivalent static analysis and let you know
Message 6 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
This is going to be your decision  Smiley Wink
Artur Kosakowski
Message 7 of 14
Μηχανικος
Yes ofcourse, i will need to do some research on that. maybe other experienced professionals can share their ideas.
Message 8 of 14
Μηχανικος
I just had a thought, eurocode8 suggests reducing the stiffness of the elements by 50% for seismic analysis due to cracking.
Which i did, Dont you think that is reasonable to assume that the stiffness of the supports also reduces during an earthquake due to cracking therefore it should be considered in the model?
Message 9 of 14
Μηχανικος
Message 10 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Μηχανικος
As Poland is not in the seismic zone I have limited experience in this area. I hope somebody else will give you some good advice.
Artur Kosakowski
Message 11 of 14
Μηχανικος
Hi, its been a long time but i never found the answer to this question, my writing is in red
@Artur.Kosakowski wrote:
Hi @Μηχανικος
1. My understanding is that you expect the column to be of a smaller size.
1. Yes I expect the column to be of normal size. Obviously there is an issue if such a large section is required.
2. If so, from my experience usually the issue is not with the RC Design but with the values of internal forces you get for a column. Are they as you expect them to be or larger?
2. So if the problem is about the internal forces, why do i get this issue? why there is an issue with the internal forces and what is usually the solution?
3.Perhaps you should look at the value of the base shear for seismic analysis and compare it to the static force procedure (assuming you defined the response spectra one) or change the supports from fixed to pinned.
3. Why did you ask me to compare the base shear of the Seismic (Equivalent Lateral Force Method) with the Seismic (Design response spectrum)
Message 12 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Μηχανικος
The results you obtained are for a model as defined. If e.g. it is created in such a way it behaves differently than expected (e.g. missing releases or supports; ignored instability, wrong seismic analysis parameters etc. ) then the column size and its reinforcement will also be different than expected. As you should know the estimated values of forces in the column the question are the obtained values in this range?
To check if the results of the seismic analysis are in the expected range.
Artur Kosakowski
Message 13 of 14
Μηχανικος
2. "The results you obtained are for a model as defined. If e.g. it is created in such a way it behaves differently than expected (e.g. missing releases or supports; ignored instability, wrong seismic analysis parameters etc. ) then the column size and its reinforcement will also be different than expected. As you should know the estimated values of forces in the column the question are the obtained values in this range?"
2. The results of the external forces are reasonable, however the results of the internal forces given in the RC Design Module -> Provided Reinforcement -> Column Results Tab are excessive.
could this be due to the layout and behaviour of the structure during an earthquake?
3. "To check if the results of the seismic analysis are in the expected range."
3. Yes the results of the seismic analysis are in the expected range. Below are the checkings i make to ensure that the analysis and input loads are correct.
1. Selfweight:
First i check the total selfweight of the frame (given by robot in Stories Table -> Values -> for the selfweight Load Case) against hand calculations.
    Checking 1 is OK.
2. Dynamic Mass:
Then i check the dynamic mass (given by robot in Stories Table -> Values -> for the Modal Load Case) against hand calculations.
     Checking 2 is OK.
3. Seismic Base Shear:
Then I check the seismic base shear acting on the columns & walls (given in robot in Stories Table -> Reduced forces -> for the Seismic Load Cases in X & Y directions) against hand calculations.
I also check the shear force given by Robot in Results -> Diagrams for bars
     Checking 3 is OK.
Message 14 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Μηχανικος
So my understanding is that the forces in the column are correct (as expected). If so, could you attach your hand calculations for the indicated column from Robot model (size and reinforcement) for this set of forces co that we could try to look for differences?
Artur Kosakowski