Shear force results at member nodes

Shear force results at member nodes

david.mackie29GRW
Explorer Explorer
1,905 Views
13 Replies
Message 1 of 14

Shear force results at member nodes

david.mackie29GRW
Explorer
Explorer

Hi,

I have modelled a steel frame and I am trying to view shear forces at member ends/connections/nodes.  The viewer appears to show Fz as kN/m along each member instead.  Is there a way of viewing member reactions at nodes?

Thanks

0 Likes
1,906 Views
13 Replies
Replies (13)
Message 2 of 14

Rafacascudo
Mentor
Mentor

Every graphic results for bars can be shown through Results/Diagrams for bars...

Rafael Medeiros
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 3 of 14

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @david.mackie29GRW 

 

Could you attach a screen capture showing what you mean? The shear forces Fy and FZ for bars are always in force unit (kN) rather than kN/m which seems like value of load instead.

 

 



Artur Kosakowski
0 Likes
Message 4 of 14

david.mackie29GRW
Explorer
Explorer

Hi @Artur.Kosakowski 

Please see attached screenshots.

I'm sure this is straightforward, but I cannot find the menu/button to do this.

For example, I'm expecting the vertical reaction from the end of member 283 will be about 500kN from the worst-case load combination.  How do I display/view this?

 

(I have removed the applied loads from the screenshot which were in kN/m - ignore my comment on this!)

 

Model Overview.JPGmodel with  Fz.JPG

 

 

 


 

0 Likes
Message 5 of 14

david.mackie29GRW
Explorer
Explorer

Might have figured this out with "detailed analysis".  I'm surprised Fx gives the vertical forces, rather than Fz though.

 

 

bar shear.JPG

0 Likes
Message 6 of 14

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @david.mackie29GRW 

 

Internal forces in bar elements are in their local coordinate systems rather than the global one with the local X being along the bar. Shear forces in bars are FZ and FY respectively. 

 

Mind that for a truss you don't have shear forces in chords as they are distributed to posts and diagonals whereas bending is 'replaced' by tension and compression in these very chords therefore you see FX and very small FZ.

 

If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.



Artur Kosakowski
0 Likes
Message 7 of 14

david.mackie29GRW
Explorer
Explorer

Thanks @Artur.Kosakowski,

Understood about the axis, and yes there is very little Fy and Fz in the chords as they are in compression or tension.

To obtain the end reactions from these chord members, is the only way to interrogate the forces in the supporting column or beam?
0 Likes
Message 8 of 14

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @david.mackie29GRW 

 

I'm not sure if I understand what do you need exactly ( I assume it is not FZ value at the end of the bar as you have these values in the Forces table directly). Could you attach a sketch that illustrates your question?



Artur Kosakowski
0 Likes
Message 9 of 14

david.mackie29GRW
Explorer
Explorer

Hi @Artur.Kosakowski,

Yes, it is that simple! 🙂 It is just the shear force at the end of the member I need so I can complete a hand calculation to check the bolted connection.

When I look at the Forces table (taking member 283, at node 272 as an example from above), the max values I am getting for Fz are not what I expect for the shear force.  This should be about 300kN.  Please see image attached.

 

forces.JPG

 

When I look at the supporting column (member 280) this has a 317kN axial force (albeit not all of this will be from member 283).

 

How can I view the end member reactions/shear forces?

 

0 Likes
Message 10 of 14

Rafacascudo
Mentor
Mentor

Reactions tab on " diagrams for bars..." on Results menu

Rafael Medeiros
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 11 of 14

david.mackie29GRW
Explorer
Explorer

Hi  

Please see below when I try that...  21.7kN is not the end reaction I need - this should be circa 300kN.

Not sure what I'm doing wrong!

end reactions.JPG

 

0 Likes
Message 12 of 14

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @david.mackie29GRW 

 

How do you calculate FZ force at the chord end (beam vs. truss)?

 

beam vs truss.PNG 

If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.



Artur Kosakowski
0 Likes
Message 13 of 14

david.mackie29GRW
Explorer
Explorer

Hi 

 

In the example you show above - I can see how you show reactions at supports.

Also, for simple beams - Fz gives the reaction at the beam end - which makes sense.

 

But this isn't clear for the reaction/shear force at the end of chord of a truss, which in my case is away from the supports.

0 Likes
Message 14 of 14

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @david.mackie29GRW 

 

I set the display in such a way that the diagrams are shown only for selected bars and nodes. If I add posts and diagonals you will see that for the truss the load is distributed to supports via axial loads in posts and diagonals rather than shear in chords.

 

shear vs axial force.PNG 

If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.



Artur Kosakowski
0 Likes