SEISMIC ISOLATED BUILDING

StefanoPasquini6790
Advisor
Advisor

SEISMIC ISOLATED BUILDING

StefanoPasquini6790
Advisor
Advisor

Good morning at all,

 

I'm designing a seismically isolated building with the seismic devices placed in the top of the column of the ground floor. Well, the model it works perfectly, I made all the manual checks to validate it.

 

My question is: the storeys that are placed over the base isolation devices have a displacement of about 300 mm, how can I keep in count the effect of this displacement as load eccentricity in the top of the rc column?

 

Thank in advance!

 

 


PasProStudio

www.pasquiniprogetti.eu

Structural + Detailing engineers
0 Likes
Reply
Accepted solutions (1)
797 Views
5 Replies
Replies (5)

StefanoPasquini6790
Advisor
Advisor

Hi again,

 

to be more clear in this topic, here attached two pics of a little part of the model, where it can be understood the geometry of the problem.

 

Detail of the modelDetail of the modelDisplacement in seismic conditionDisplacement in seismic condition


PasProStudio

www.pasquiniprogetti.eu

Structural + Detailing engineers
0 Likes

Romanich
Mentor
Mentor

Ciao Stefano,

 

The first solution is to shift the RC column in the direction of the biggest displacement and connect the device and column using a rigid link.

Do you find the posts helpful? "LIKE" these posts!
Have your question been answered successfully? Click 'ACCEPT SOLUTION' button.

Roman Zhelezniak

Robot Evangelist & Passionate Civil Structural Engineer

LinkedIn | Robot & Хобот | App Store for Robot
EESignature


t.sautierr
Advisor
Advisor
Second,third, fourth solution (but more time consuming) :
Second : second order analysis with peudo static forces of your seismic cases
Third : use the deformed shape update macro on your model and redo a calculation for statics vertical forces
Fourth : retrieve displacement and effort on the column and apply a moment or an excentric nodal force (keep in mind to equilibrate it at the bottom to have only moment effect) to each column in a new load case via api.

StefanoPasquini6790
Advisor
Advisor
Accepted solution

Hi everybody, and thank you for your effort.

 

I soved in a "SAFE WAY" adding a concentrated moment in the top of the rc column that have the magnitude equal to the maximum displacement in the considered direction * SLS QPR vertical force value.... I've done for the four seismic condition and added in combination....

 

Excellent result!

 

Thank you 


PasProStudio

www.pasquiniprogetti.eu

Structural + Detailing engineers

Artur.Kosakowski
Autodesk Support
Autodesk Support

Hi @StefanoPasquini6790

 

Thank you for sharing the solution with others. 



Artur Kosakowski
0 Likes