Hi I need help in changing the material in the RC component inspector section. i have tried everything I cant seem to change the concrete class to C35. I also keep getting an error for my slab reinforcement that states that: The concrete strength does not fulfill the code requirements concerning the exposure class: 24 MPa < 25 MPa - E.1(2). please see attached images and my document. I also can't figure out how to make the minimum spacing of the reinforced bar 100mm without generating error.

0 Likes
Reply
Accepted solutions (1)
481 Views
1 Reply
Reply (1)

Krzysztof_Wasik
Autodesk Support
Autodesk Support
Accepted solution

Hi @Anonymous 

I would recommend the following steps to improve results.

 

1. Correct your model geometry and mesh model again

Model is not defined precisely. Walls are not defined along bottom panel edges. It results in meshing issue and internal forces distribution then big reinforcement calculated. Structure is regular and mesh should be regular as well.

 

Example not precisely defined model

vvv.PNG

Mesh 

mesh.PNG

 

2. In Reinforcement type go to Material tab and check Material as in a structure model. Program will take C35 for reinforcement calculation.

mat.PNG

3. In reinforcement type go to SLS tab and Allow non linear creep for reinforcement calculation.

vvvv.PNG

 

4. Calculate structure,

5. Calculate required reinforcement and then

6. Calculate provided reinforcement.

 

Actually maximal required reinforcement calculated in your model is about 470 cm2/m

actual.PNG

After modifications it should be much smaller.

 

 

 

 



Krzysztof Wasik