I am trying to model a RC lift pit that can support mezzanine column loads on top of the walls, however when I add these point loads as an edge load to the top of the panel it induces large tensile forces within the panels as seen in the image attached. Is this result correct, as this means a lot of additional rebar is required as a result?
All panels are designated as slabs and the bottom slab is ground bearing with springs defined. I assume the tensile loads are induced in the walls because the rebar will be activated when the ground slab deflects downwards due to the point load on the wall, this appears to be supported by the results when the wall bottom edge has fixed supports then the tensile forces are much reduced with only a few stress concentrations occurring at panel corners/ intersections.
On the other hand, if the wall was just mass concrete the column loads would be transferred to the slab without an issue but then there are bending moments out of plane to consider due to soil/ water pressures.