Modal mass missing in higher mode shapes
MRCH94D9W
MRCH94D9W
Hi
I'm experiencing some incorrect modal masses calculated by Robot 2020.
To investigate I have made a 10m simply supported IPE100 beam, and checked the mode shapes.
As per analytical calculation, all "sinus mode shapes" should have the modal mass of: 1/2*8.34kg/m*10m = 41.7kg
This fits quite well with mode shapes 1-3. However, when looking at mode shape 4, the modal mass drops to 26kg and even further beyond that.
I have traced it to what I think is a discrepancy in the normalized eigenvectors.
Looking at mode shape 1 the normalized eigenvector has a value from 0 to 1, mode 2-3 has a value from -1 to 1, but mode 4 has values from -0.8 to 0.8.
So, why this incorrect normalization, and is that what causes the missing modal mass?
I'm using Lumped mass matrix with rotations. I have tried discretizing the beam by 10-100 nodes, but it doesn't affect the modal mass to the extend I need.
The eigenfrequencies seem to be correct though.
I have attached the model as a zip file, as the forum doesn't allow me to attach it as *.rtd file.
Kind regards
Martin
Simau
Hi @MRCH94D9W
Could you do the same analysis for the example attached?
M. Agayr
MRCH94D9W
Same thing happens 😕
Simau
And what about this example?
Look at mode 1-6 and mode 7-20
Add another beam and look what happens
M. Agayr
MRCH94D9W
By introducing the extra beam you have changed the static system.
Only the odd modeshapes are comparable, i.e. 1 = 1, 2=3, 3=5, 4=7 etc. and the modal mass should be divided by 2 to be comparable.
We still see the same issue
  • Shape 1 (1) mZ = 81kg --> 40.5 kg
  • Shape 2 (3), mZ = 90kg --> 45 kg
  • Shape 3 (5), mZ = 81 kg --> 40.5 kg
  • Shape 4 (7), mZ = 53 kg --> 26.5 kg
Simau
I must look more closely at this subject, but not for now
Maybe someone else has an idea
M. Agayr
MRCH94D9W
Can someone from Autodesk please address this issue?
Would be prudent to identify whether this is a modelling issue or if it is an error in the software.