Instability in rigid link nodes
Wendy_smith
Message 1 of 23
Wendy_smith
I have placed rigid links in my model. I have W10x33 beams resting on top of W24 girder beams. The W10's are bolted to the top flange of the W24's. I placed a rigid link between the nodes for the bolt. When I run the calculation for just dead load, I have instabilities in the nodes on the W10's for the rigid link. Iam not sure what I am doing wrong. I have attached my model and a screenshot. Any help would be greatly appreciated.
Replies (22)
Message 2 of 23
Simau
@Wendy_smith
Set Bolt rigid link like this
M. Agayr
Message 3 of 23
Wendy_smith
@Simau,
Thank you for your response. Why am I setting my Bolt rigid link like that? What does that do?  What does a Welded rigid link look like? Thank you for the help.
Message 4 of 23
Simau
@Wendy_smith
In your model, you set bolt as below
Which means that your bolts don't block anything (Ux Uy an Uz are free)
In my bolt setup, to ux uy uz, i added rx to avoid instability. Bolt rx corresponds to the strong W 24x104 inertia (UY)
As below
M. Agayr
Message 5 of 23
HoshangMustafa
@Simau
Bolt rx corresponds to the strong W 24x104 inertia (Iy)
Message 6 of 23
Simau
@HoshangMustafa
Sorry about the typo.
Correct, its Iy
M. Agayr
Message 7 of 23
HoshangMustafa
Hi @Simau
Using ux uy uz, and rx blocked directions for a rigid link, how one can design the connection manually? I think these blocked directions are delivered to the connection. So how one can use these blocked directions to design the connection manually?
Message 8 of 23
Simau
@HoshangMustafa
Below a workaround, but maybe there is a quicker solution.
Select all W10 33 members, then look at fz diagram to calculate reaction at these nodes.You may then design your bolts under these reactions.
To be conservative you can select all W 10 33 members and take design reaction as max Fz + Min Fz
M. Agayr
Message 9 of 23
Simau
@HoshangMustafa
Message 8 updated (you don't need to split W10 33 members)
M. Agayr
Message 10 of 23
HoshangMustafa
Hi @Simau
your attached picture:
there seems to exist 4 bolts, two on each side, correct?
In the model, there exists only one rigid link at this place, isn't it?
How one can use (one) rigid link results to design these (4) bolts?
Message 11 of 23
Simau
@HoshangMustafa
Yes there are 4 bolts (but its only an example). A bolt is designed with Reaction/4
You may use the classic scheme:
M. Agayr
Message 12 of 23
HoshangMustafa
Hi @Simau
This is for gravity loads. For lateral loading (i.e., wind load) how rigid link can be applied if there is eccentricity?
Message 13 of 23
Simau
@HoshangMustafa
Please complete your model with loads you need and create combiations. If you apply wind loads to claddings, efforts will be mostly parallel to local axis Z of the purlins.
Look at "reactions" in local axis  x y z , you will find that the efforts in the x and y directions are negligible.
M. Agayr
Message 14 of 23
HoshangMustafa
Hi @Simau
ignore lateral load, assume gravity load as follow:
Can rigid link simulate this condition?
Message 15 of 23
Simau
@HoshangMustafa
Yes, just add Rz as blocked direction in bolt parameters
M. Agayr
Message 16 of 23
HoshangMustafa
Hi @Simau
My concern was about the share of each bolt from the load, i.e., rigid link simulating for this case (a group of bolts, each bolt receiving a share of load based on its distance from the load).
Message 17 of 23
Simau
@HoshangMustafa
It's not possible.
The rigid link will give you the the whole torsional moment , but not the sharing of this moment between the bolts. You have to calculate the distribution manually.
You may  try a small model simulating this connection (see model attached)
M. Agayr
Message 18 of 23
HoshangMustafa
Hi @Simau
Can you upload the model with earlier version (2018)?
Message 19 of 23
Simau
@HoshangMustafa
Very sorry, but old versions are no longer installed here.
M. Agayr
Message 20 of 23
Simau
@HoshangMustafa
here is what I modeled.
A steel plate on 6 supports subjected to a torsion moment of 100 kNm
M. Agayr