Hello everyone,
I contact you because I have a problem about the assemblies in Robot.
I don't get the same calculation by hand and by robot...
It's for the column web in transverse compression:
By hand: Fc,wc,Rd=1*1*160mm*6mm*235N/mm²=225.6 kN
By Robot: Fc,wc,Rd=206.17 kN
Can somebody help me to find this mistake ?
Thank you for the answer
Solved by Artur.Kosakowski. Go to Solution.
I attached you my file of robot.
Can you check if there are problems in steel connections ?
Thank you for the help ! 🙂
Thank you for watching the file mustafa !
I cannot do anything to remedy this problem so ?
I think the software does a lot of data approximation.
Hi @Anonymous
The difference is that you used the rounded values for your hand calculations (as set to be displayed in the calculation note by the display precision you set in Job preferences) whereas RSA internally uses the not rounded values:
If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.
Many thanks for this information its very helpful.