help with Slab reinforcement values
Message 1 of 11
I don't understand the value I am getting in my reinforcement graph, the table show different values C25 AND the graph shows D=12 mm at 250 mm can any one help me what should I adopt. picture attached
Replies (10)
Message 2 of 11
Artur.Kosakowski
Autodesk Support
Autodesk Support
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
Message 3 of 11
1- Yes I can see the c20 bars but shall I ignore the 12 *240 appears on the graph or they should be included in my design in addition to the C20 bars  as I set up my design to include only C20 bars .
2- something else occurs, I am getting this error message?  how can I get rid of it. (as attached)
Message 4 of 11
Artur.Kosakowski
Autodesk Support
Autodesk Support
1. Ignore the values from "maps". They don't correspond to the distribution of reinforcement in zones which is displayed in the way I indicated on the screen capture from my previous answer.
2. Check if one of the zones for top reinforcement there is the information that provided reinforcement is smaller than the required one. If not attach the model and indicate which plate (if there is more than one you generated reinforcement for) to look at.
Artur Kosakowski
Message 5 of 11
1- thank you.
2- I did check that the provided reinforcement is always larger than the required one in top and bottom of the slab.  I can't attach the model as it is confidential but I can send some photoshoot if that would help.
3- Am I able to change the orientation of the reinforcement to span 45 degree from the X or Y coordinate? (my slab is 45 degree from the x coordinate but still robot consider the reinforcement either by X or Y direction.
4- How can I change the bar diameter for each zone separately,  as u can see from the attached paper, all have the same diameter with different spacing.  do I need to do it manually? and how. thanks
Message 6 of 11
Artur.Kosakowski
Autodesk Support
Autodesk Support
Will you be allowed to send a file "reduced" to the slab in the RC Provided Reinforcement module only (with no model itself)?
Do you want to do so for the entire panel or its part only?
Yes by editing the blue values for diameter and spacing originally assumed for each of the zones.
Artur Kosakowski
Message 7 of 11
2- I don't know how to delete the model and keep reinforcemet only .....I will try.
3- I want to rotate the x direction of the whole panel 45 degree just for reinforcement direction. not part of it.
4- thanks for the solution.
Message 8 of 11
Artur.Kosakowski
Autodesk Support
Autodesk Support
Calculate the provided reinforcement for the panel
Save the file
Switch back to the model
Select and delete the whole structure
Delete it
Save the file under a new name.
Start a new project
Open the file you saved and check if there is no data that you cannot share
If it's OK sen the rtd file
3.
Rotation of  the local X of  a panel panel
Rotation of the reinforcement direction without changing the local X of a panel
Rotation of the panel exported to the RC Provided reinforcement module
Artur Kosakowski
Message 9 of 11
Hi  Artur,
Thanks for your very clear answers.
I attach the whole model for you to have a look.  I am still having errors in the reinforcement.
Regards
Message 10 of 11
Artur.Kosakowski
Autodesk Support
Autodesk Support
As the edge of a slab are slightly inclined some bars start or terminate with larger distances to the edges. You can manually edit some of the rebars or check the locations of the reported issues and then decide if you just want to ignore them.
Artur Kosakowski
Message 11 of 11
Thank you