fire design
fire design
fire design
column 58 with permanent load
column 233 connected with column 58 (same displacement)
fire design:
for column 58: temperature/time domain and resistance domain give the same results:   Tcrit = 692°C at 28.7min.  -  at 28.7min,  Ed = Rd
for column 233 temperature/time domain and resistance domain give not the same results:  Tcrit = 350°C at 10.6min.  -  at 60min,  Ed = 0.75 Rd, Tmax 934°C.
Tmax > Tcrit but Rd>Ed
why column 233 not axially loaded does non have the same results in the two calculation methods?
thank you
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Anonymous
Could you attach both the model and screen captures which illustrate the description you provided?
Artur Kosakowski
Temperature/time domain method
[cid:image002.jpg@01D39E8D.5F7B2680]
Resistance domain method
[cid:image006.jpg@01D39E8D.5F7B2680]
For HEA500 I get the same sesults for both method (resistance, Tcrit and time limit).
For IPE600 : for resistance method: resistance verification 0.78, reached temperature = 934 °C; but for Temperature/time domain method Tcrit = 350 °C
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Anonymous
You missed the attachments. You may try to zip them before attaching.
Artur Kosakowski
test file for fire design
Artur.Kosakowski
Autodesk Support
Autodesk Support
Hi @Anonymous
Bar 233 is of class 4 therefore the critical temperature is limited on 350 whereas for the resistance domain method has got no such limit therefore IMHO you can't compare results.
If I managed to answer your question(s) press the Accept as Solution button please. This will help other users to find solution(s) much faster. Thank you.
Artur Kosakowski