Exceptional load

Exceptional load

Anonymous
Not applicable
486 Views
3 Replies
Message 1 of 4

Exceptional load

Anonymous
Not applicable

During dimensioning the foundation combinations do not take into account exceptional load. When we highlighting a combination containing an exceptional load then we see the corresponding values of force for this combination, while they do not appear under the foundation drawing above.

487 Views
3 Replies
Replies (3)
Message 2 of 4

Krzysztof_Wasik
Autodesk Support
Autodesk Support

Hi @Anonymous 

 

I made simply check using model defined from scratch and my results seems to be reasonable

 

Could you please send your file

 



Krzysztof Wasik
0 Likes
Message 3 of 4

michal.245
Explorer
Explorer

I have the same problem, and still dont know what to do, to solve it. I've tried everything but it's pointless.

0 Likes
Message 4 of 4

Krzysztof_Wasik
Autodesk Support
Autodesk Support

Hi @michal.245 

 

ACC loads are not teken into account while spread footing stability check in Robot Structural Analysis

But ACC combination  after generation using auomatic combination tool can be changed in ULS combination and then will be used while footing stability check

 

Short description of combination update process

  1. Generate automatic code combination with accidental combinations included using  Manual Combination generate option.
  2. Open Load > Combination table.
  3. Go to Edit tab.
  4. With right mouse button open Table column and check on Type of Combination, then OK.
  5. Select all Accidental combinations.
  6. With right Ctrl pressed select Combination type column.
  7. With right mouse button select Fill Special.
  8. Change selected combination type to ULS.
    Accidental combinations, changed into ULS will be used for stability check in RC spread footing module 

 

 

 

 

 

 

 



Krzysztof Wasik