Combination Cases
Combination Cases
Message 1 of 8
Combination Cases
I have 3 simple cases:
  • dead load, super dead, live load
I run these as Non-linear Pdelta.
Then in my combination case, do I need to set it to be non-linear Pdelta also??
Or can the combination be Linear?  I thought that the combination just "assembles" forces generated inthe simple combinations, so the type of combination is irrelevant?
Tony
Replies (7)
Message 2 of 8
Artur.Kosakowski
Autodesk Support
Autodesk Support
If you have a non linear object in your model (cable, tension only bar, unidirectional support) then all load cases and combinations are non linear by default. Otherwise by default they are linear and you have to set them (each of them) to be non linear or P-delta.
Artur Kosakowski
Message 3 of 8
Artur,
What I mean is:
I'm running Pdelta to take into account second order effects, not for cables, tension only etc.
So the combinations are by default linear.
But if the linear combination contains non linear cases, can it be kept as linear?  Will it combine non linear simple cases differently to a combination definaed as non linear also?
Message 4 of 8
Artur.Kosakowski
Autodesk Support
Autodesk Support
Tony,
When you set non linear (or P-Delta) analysis for simple cases manually changing them from linear static then yes. It is your decision what kind of analysis you want to use for each of the combinations. If there is any non linear object in the model all simple load cases and combinations will be automatically set as non linear too.
Artur Kosakowski
Message 5 of 8
Artur,
I just made a simple test case.
If i run three simple cases as linear, then a combination of the three as non linear + P-delta, I get the same result as if I run EVERYTHING non linear + P-delta.
This is not what I expected to happen, I thought the simple cases would need to set P-delta to be included in a P-delta combo.
The model I am running at work took 5 hours to run today.  I ran simple cases 1-5 as P-delta, then all of the combo's as P-delta too.  So tomorrow, I can put all 5 simple cases back to linear and take half the time off the run.  Smiley Happy
Thamks
Message 6 of 8
Artur.Kosakowski
Autodesk Support
Autodesk Support
This is correct because in both cases you run the combination as non linear. The results of simple load cases are irrelevant (they could even be set as auxiliary and not calculated at all) as each non linear combination is calculated separately (as if being a simple load case with loads defined in all simple load cases that define it multiplied by their load factors). On the other hand a linear (static) combination is based on the superposition of the results of simple load cases therefore if you run 3 simple load cases as non linear and then you create linear combination its results will be different comparing to scenario when you run linear static for these simple load cases and then you combine them linearly.
Artur Kosakowski
Message 7 of 8
gustavo_c_vasconcellos
Dear Artur,
what is your recommendation for a 20 levels concrete buiding in respect P-Delta? Should I include one combination non-linear P-delta, or should I set all loads  as non-linear P-Delta?
Gustavo
Message 8 of 8
Artur.Kosakowski
Autodesk Support
Autodesk Support
For non linear analysis the results of simple load cases are irrelevant as each of the combination is calculated separately (for linear static the results of a combination is just the superposition of the results of simple load cases used for its definition). The simple load cases stand in such case merely as load definition and can be set as auxiliary to reduce the size of results. In other words usually there is no point to run simple load cases as non linear (P-Delta).
Artur Kosakowski