Hi Artur,
Re brain capacity, Robot support staff - yourself included
- are doing a tremendous job by handling a large variety of topics, providing sound advice in a timely manner and with impeccable manners. Well done to you all and THANK YOU again.
====
Further on the AS4100 design check.
The length of the verification segment including the section at 1.0L is also incorrect. There is no "segment" of that length along the bar, where "segment" is as defined in AS4100.
I suggest that a "segment (in a member subject to bending)" is not necessarily the length of a bar in between two consecutive restraints of the same flange but between two consecutive sections that are fully or partly restrained or the length between an unrestrained end and the adjacent cross-section which is fully or partly restrained. Refer again at the definition given by AS4100 page 11.
In regards to considering a restraint at the location along the bar where the bending moment is zero, AS4100 does not explicitly accept it.
AS4100 deals with the shape of the bending moment distribution by using the moment modification factor alpha_m - such as 5.6.1.1 (a) (iii) for open sections with equal flanges.
In supporting this view is the table 5.6.1 where various bending moment distribution show a zero bending moment location within a "segment" .
If there was a restrained section at every zero bending moment location then some of the diagrams shown in table 5.6.1 would be obsolete.
Furthermore - I'm almost done - I suggest that the design bending moment in the segment under consideration should be the value at the "critical section" as defined in 5.3.3 and reproduced below:
5.3.3 Critical section The critical section in a segment shall be taken as the cross-section which
has the largest value of the ratio of the design bending moment (M*) to the nominal section capacity in
bending (Ms) (see Clause 5.2).
===
Please review and if agreed submit the above to the dev team for their consideration.
With thanks.
Max