I am frustrated. I have a 12480V, 3 phase Medium Voltage Switchgear called MV3. And then I have a 3 phase 12480-600Y/347V Transformer (TX-PB) that I want to power up from (circuit to) switchgear MV3. When I do this, it provides me with only 1 circuit instead of three, for example MV3-1 instead of MV3-1,3, 5.
How do I solve this issue and have 3 circuits powering my 3 phase transformer?
I have already done my voltage definitions and Distribution System settings.
In my emergency section, I have a 3 phase 600/347V generator G1 powering a 3 phase 600/347V panel E1. When I circuit E1 to G1 it provides me with 3 circuits: 1, 3, 5. And when I power a 600-208Y/120V transformer TX-2E1 to E1, I get 3 circuits: 1, 3, 5.
So why is my normal power TX-PA not powering up with 3 circuits to MV3? The properties on TX-PA states that is has 3 poles, 3 phases and 4W.
The Electrical Connector must not be configured properly. Open the Family for editing (right-click on it and select that option) and then select the Primary Connector, which is the large green circle with a cross. Under Properties, the Number of Poles parameter should be linked to the Family Parameter that controls this, which should be of the same name. If this value is linked to a Parameter, then the little gray button to the right of it should display an equal sign. If not, click that button and select the Parameter from the following list. Load the Family back into the Project, overwriting the previous definition.
Hi Corey,
I have looked at both the transformer and the switchgear and they are both stating 3 and they both have the "=" sign on the right in the properties. See the attached images.
Any other ideas?
Jamie