Watts Per Square Foot - Working in specific instances
Message 1 of 8
I have a simple Watts/sq ft schedule in REVIT that I can't get to work in a certain project. It's literally just adding the Actual Lighting Load Per Area parameter from a SPACE schedule.
Everything to the eye seems to be the same in both projects. What am I missing on this one project that isn't allowing it to fire?
It has spaces defined. The lights are programmed the same.
Thoughts?
~BMC
Replies (7)
Message 2 of 8
CoreyDaun
The cause may be that Load Calculations have not been activated for the project. Go to Electrical Settings » Load Calculations and make sure that the box is checked for 'Run calculations for loads in spaces'.
⁞|⁞ Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums. Thank you!
Message 3 of 8
It's checked.
I did notice that VOLUME isn't being calculated for the space. I'm curious if that could be hindering the calc.
~BMC
Message 4 of 8
CoreyDaun
Disabling Volume calcs did not affect my schedule. So ALL of your spaces are coming up with a value of 0 W/ft²? Cut a Section and verify that the fixtures are not somehow above and outside of the Space.
Message 5 of 8
Tried all that too. I programmed the space to extend to the level above.
It's odd that it's working in a little test project that I threw together for training, but isn't working in a project that actual architects set up the model. I would assume as an engineer, my model should be the incorrect one 🙂
Message 6 of 8
CoreyDaun
So, no matter what fixture is used, for every Space, you are getting 0?
If you draw a separate Space (isolated Space Separators) off to the side and place some lights in that, does it still read 0?
Message 7 of 8
I can try your second idea.
To your first question, I actually took the fixtures out of the one that is working and placed them in the project that was not and it did nothing.
Message 8 of 8
Problem solved.
The connector in the fixture was set to OTHER and not LIGHTING. Once switched, the calcs worked.
Thanks for your help.
~BMC