System analysis 2022

gopigopi766
Participant
Participant

 I use system analysis to get hvac system loads and sizing report when analytical systems was created. its shows "energyplus simulation did not generate a report for systems analysis" .but without analytical systems it give load report.what mistake I did? Pls explain. Without analytical systems it 

0 Likes
9,490 Views
33 Replies
Replies (33)
Message 2 of 34

Kevin.Lawson.PE
Advocate
Advocate

What does the error file in your temp directory say?  You can check it like this:

 

If a systems analysis fails, check the eplusout.err error log located in the system temp folder.

In Windows Explorer, enter %temp% to quickly open the temp folder and search for a folder with the same name as the selected analysis workflow. Depending on your Windows security settings, you may have one more system-generated folder.

The folder path will look similar to this: C:\Users\<login>\AppData\Local\Temp\3\fbf31253-58bb-4d1a-b5db-ae57c7b3aee2\HVAC Systems Loads and Sizing. The eplusout.err log file is located in the \run sub-folder.

 

From here: https://knowledge.autodesk.com/support/revit-products/troubleshooting/caas/CloudHelp/cloudhelp/2021/...

-Kevin Lawson, PE
www.rippleengineeringsoftware.com
Revit heating and cooling load calculations in one click!
0 Likes
Message 3 of 34

gopigopi766
Participant
Participant

It shows like this, how to solve this

0 Likes
Message 4 of 34

Kevin.Lawson.PE
Advocate
Advocate

The critical error is at the bottom of the of the text file, scroll down or attach the file. 

-Kevin Lawson, PE
www.rippleengineeringsoftware.com
Revit heating and cooling load calculations in one click!
0 Likes
Message 5 of 34

gopigopi766
Participant
Participant

i attached the file pls check it .i didn't understant.

0 Likes
Message 6 of 34

Kevin.Lawson.PE
Advocate
Advocate

Your AHU-01 preheat coil has an inlet air temperature higher than the outlet air temperature, which is impossible for a heating coil.

 

From the text file:

** Severe ** For Coil:Heating:Water, AHU-01 PREHEAT COIL ** ~~~ ** the Rated Inlet Air Temperature must be less than the Rated Outlet Air Temperature. ** Fatal ** GetWaterCoilInput: Errors found in getting input. ...Summary of Errors that led to program termination:

-Kevin Lawson, PE
www.rippleengineeringsoftware.com
Revit heating and cooling load calculations in one click!
0 Likes
Message 7 of 34

gopigopi766
Participant
Participant

sorry ,i didn't know how to solve this ?,pls give solution

0 Likes
Message 8 of 34

gopigopi766
Participant
Participant

i didn't set any inlet and outlet temperature. how it will take from where?

0 Likes
Message 9 of 34

Kevin.Lawson.PE
Advocate
Advocate

Did you ensure that the water loop assigned to the preheat coil is a heating water loop? 

-Kevin Lawson, PE
www.rippleengineeringsoftware.com
Revit heating and cooling load calculations in one click!
0 Likes
Message 10 of 34

gopigopi766
Participant
Participant

yes

0 Likes
Message 11 of 34

gopigopi766
Participant
Participant

i attached a project file. pls give the solution .

0 Likes
Message 12 of 34

gopigopi766
Participant
Participant

I removed the waterloop of AHU preheat coil.but still its shows same error ''inlet temperature is must less than outlet temperature''.how to solve .pls give solution .

0 Likes
Message 13 of 34

Kevin.Lawson.PE
Advocate
Advocate

Start with as simple of a system as you can and build from there. 

 

Try to remove all systems and just have all your analytical systems unassigned.  Then run the "HVAC Systems Loads and Sizing".  If you can get that to run try all electric heating and direct expansion cooling.  If you can get that to run, add in water systems. 

-Kevin Lawson, PE
www.rippleengineeringsoftware.com
Revit heating and cooling load calculations in one click!
0 Likes
Message 14 of 34

Anonymous
Not applicable

Never it's work

0 Likes
Message 15 of 34

iainsavage
Mentor
Mentor

I'm finally trying to get to grips with systems analysis.

I've been following the tutorial here: https://www.autodesk.com/certification/learn/course/revit-system-analysis-mechanical-design-professi...

When I got to the part where you run the systems analysis it failed with the error in this post.

There is no eplusout.err error file as far as I can see - couldn't find it.

According to this support article lack of an error report indicates that two spaces share the same zone equipment.

After trying several attempts with no success I built a test model with four walls, roof, floor, door and windows, one space, zone equipment is unit heater with electrical resistance coil, all energy settings etc seem to be okay.

iainsavage_0-1638484764038.png

 

I've tried in in both 2021 and 2022, all updates applied.

No matter what I do I cannot get the software to generate a systems analysis report.

 

Any clues as to why?

Message 16 of 34

val-fournier
Community Visitor
Community Visitor

I am having the exact same issue. Did you find any solution? 

0 Likes
Message 17 of 34

iainsavage
Mentor
Mentor

I have an active support case with Autodesk and have been working with their support and development teams for a couple of months now to try to get a solution. It seems this is a very rare problem and is caused by some of the pre-requisite software not installing properly but so far they’ve been unable to solve it. 

I have a test model with one space and one electric heater and it won’t run the report.

The gbxml seems to generate but OpenStudio won’t run.

I think they are getting close to an answer based on some diagnostics they’ve run on my laptop (which doesn’t run the analysis despite a couple of clean re-installs) and my pc (which runs fine). 
If and when I get a solution I’ll post it here.

Message 18 of 34

fuzzylogik511RXH65
Explorer
Explorer

I get the same exact issue.  Very frustrating.  I posted my situation here:

 

https://forums.autodesk.com/t5/revit-mep-forum/systems-analysis-not-working-quot-energyplus-simulati...

 

Please let me know if Autodesk comes up with a solution.

 

Thanks, 

0 Likes
Message 19 of 34

bimsunconssgp2
Observer
Observer

I get the same issue,but it's not happening on the same model and method on other laptop with windows 10. Any relation with that?

0 Likes
Message 20 of 34

fuzzylogik511RXH65
Explorer
Explorer

I too tried the same model on Revit 2021 on a different laptop without any issue.  Seems to be related to revit 2023 and the particular laptop.