The basic premise of this work-around is that the loads are connected to the proper phase of the Panel, but the actual Circuit Numbers are rubbish. The Circuit Numbers must be done manually, more or less. The circuit section of the Panel Schedules are actually two Electrical Circuit Schedules (see below). I shall attach a sample Project file (Revit 2014) as well as walk though this cumbersome process.
#1. Prepare the Panel and Circuit Electrical Devices
The first thing to do is to select the single-phase Panels and change "Max #1 Pole Breakers" to double what you want it to be. This will account for the complete disuse of the B Phase. Next, create a Panel Schedule using your single-phase Panel Schedule Template, which will show A/B Phases. Prior to circuiting, place a SPACE into every B Phase load and lock it. I just click on the first line, hit "Assign Space", then "Lock", hit the down arrow twice, and repeat. Now create your Electrical Circuits and all of them will only connect to the A Phase.
One of the downsides to this method will be the application of Spaces and Spares, since the circuit section of the Panel Schedule will not be used. So, attached is a Family called "Electrical Proxy Load" which contains an Electrical Connector and parameters. The Category of this Family has been changed to 'Electrical Fixtures'. Place an instance of this and connect one to the Panel to represent each Spare or Space.
#2. Alternate Circuit Numbers
Of course, by omitting the B Phase, the Circuit Numbers will skip, so we cannot use the Circuit Numbers assigned by Revit. The first thing to do is to add a Shared Parameter (Integer), named something like "CKTnumber1Ø", as a Project Parameter that applies to both the Electrical Fixtures and the Electrical Circuits Categories. Add this Shared Parameter to an Electrical Fixtures Tag in order to report the "correct" Circuit Number. Note that it is not possible to do this using the Wires Category.
A Schedule will be utilized to control the new Circuit Numbers. Create a new Electrical Circuit Schedule and include any Fields you wish but be sure to at least include "Panel", "Circuit Number", and your Shared Parameter. Set the Sorting/Grouping to "Panel" (Header) and "Circuit Number". The formatting doesn't matter, but you can hide the "Panel" Field. Hit 'OK'. Here is part of the manual labor; the Schedule will be sorted by the wonky Revit Circuit Numbers. In the column for your Shared Parameter, just enter the values 1, 2, 3, 4, etc. all the way down.
Another Schedule must be created and managed in the exact same way, except that this one will be an "Electrical Fixture Schedule". This is duplicate work, but it is the only way I have found to represent the new Circuit Numbers on the electrical plans.
#3. Creating the Panel Schedule
Duplicate your normal single-phase Panel Schedule Template and name with the suffix "Header Only" and edit this Template. For all of the Circuit Rows below the header: remove all Parameters possible (and replace the column header text), remove all borders and shading, set the text to 1/512" (but no smaller) and justified to Top Left. Under 'Set Template Options', set the "Number of slot shown:" to Fixed Value. This exact number will have to be tweaked later to get the appropriate gap size.
Create a new Electrical Circuit Schedule named "CKTs [Panel] Odd" and include "Panel" and the same Fields that would be shown in your Panel Schedule (in that order); use your Shared Parameter in place of the normal Circuit Number. Also, create a Calculated Value named "EvenCKT" with the formula:
CKTnumber1Ø / 2 = roundup(CKTnumber1Ø / 2) where "CKTnumber1Ø" is the name of your Shared Parameter.
Set the Filter to "Panel" "equals" and enter a specific panel name. Set the second Filter rule to be "EvenCKT" "equals" "no". Sort by your Shared Parameter. Hide the "Panel" and "EvenCKT" Fields. Set the Appearance to match your Panel Schedule and disable "Show Title" and "Show Headers".
Open a Panel Schedule View and set the Template to the "Header Only" Template. Place it on a Sheet View, and then place the newly created Electrical Circuit Schedule into the gap of the Panel Schedule. Adjust the column widths to match the Panel Schedule's widths, it will take up half of the horizontal width of the Panel Schedule. Once this is set, duplicate the "ODD CKTs" Schedule, reverse the order of the Fields, and modify the second Filter to "EvenCKT" "equals" "Yes". Place it and the column widths will be correct. Modify the Panel Schedule Template to adjust the gap as needed.
These "ODD" and "EVEN" Electrical Circuit Schedules must be duplicated for each applicable Panel. Just modify the specified Panel Name in the Schedule's Filter. It's very easy after the first ones are created - you only have to correct the column sizes once.
Phew!
Corey D.
──────────────────────────────────────────────────────────────────────⁞|⁞ Please use
.Accept as Solution and
Give Kudos as appropriate to further enhance these forums. Thank you!