Revit MEP

irfankhan888969
Explorer

Revit MEP

irfankhan888969
Explorer
Explorer

I am  trying to add the  boiler to a hydronic piping system A warning appears and the boiler cannot be added to the system. Why is this happening?

0 Likes
Reply
313 Views
7 Replies
Replies (7)

RobDraw
Mentor
Mentor

How are you trying to add it to the system?

 

Do the connector properties in the boiler correspond with the system?


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.

irfankhan888969
Explorer
Explorer

Both properties are different , 

 

When I draw the pipe , in properties panel system classification is grayed out 

0 Likes

RobDraw
Mentor
Mentor

Share a portion of the model that exhibits the issue.


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.
0 Likes

irfankhan888969
Explorer
Explorer

irfankhan888969_0-1629135513451.png

 

0 Likes

irfankhan888969
Explorer
Explorer

irfankhan888969_0-1629135707517.png

 See system Classification 

 

0 Likes

irfankhan888969
Explorer
Explorer

Boiler connector properties is Hydronic supply and when i draw pipes in plan it turned into grayed hydronic Return ??

 

0 Likes

iainsavage
Mentor
Mentor

The message in part 5 is nothing to do with the boiler - it is telling you that your pipe routing options don’t have a suitable fitting in order to join the pipes and it appears from your screenshot that there is no elbow/bend fitting in the routing options.

The other problem seems to be that you are trying to connect a supply pipe to a return connector?

0 Likes