Now here's a couple more notes. In order for any of the fittings to use the ASHRAE tables, the system must be well formed - while it may look correct from a plan view, you need to check and makre sure all of you duct is properly connected.
Here's how I caught this - the project I was testing this out on was originally developed in Revit 2014. Since we're working in 2015, I did what anyone else would do - I upgraded the file. Has this ever happened to you - you get a warning telling you a duct or pipe has been modified in the opposite direction, and the only solution is to delete the element?
That's what happened on my test file - and some of the parts were removed, causing me to have an open system. When this happens, you'll get an incorrect or missing loss value in the duct and fittings. Also, pay attention to those warnings that show up on the context tabs for the duct/part - they'll tell you if there's an error, such as no loss defined. That's usually this first hint.
To check it, create a few 3D views and sections, checking the entire system out, using the TAB keys and views. Be aware that the disconnect may not be readily obvious - the duct may look connected, but it's not.
Try this out and let me know what you find.