I have 2 boilers in parallel. when I only connect boiler 2 All flow goes through it (Connector is set to calculate) and system pressure is 9.9 psi. when I connect B-1 for some reason all flow still went through B-2 and 0 flow to B-1. but the system pressure is 7.47 psi only. In the pressure loss report I found out, it is missing the last leg to the boiler (inc. boiler, and the isolation and control valve). Then I changed the boiler connector flow to "system" and assigned it a flow of 1 for each boiler. this somehow improved things, but it only shows 8.53 psi. but it doesn't include the boiler leg (valves, boiler) in the pressure report. the reason it is so high is that setting both boilers to 1-systme flow is, on the upstream pipe it doubles the flow. So I set each boiler flow to 0.5. that gives me 7.47 again. so basically normal flow in the system, but the boiler leg is not included.
In all scenarios with both boilers connected (flow based on system flow, or connected) the system inspector doesn't show the critical path going through the boiler. In reality at full load both boilers will operate, so there is only half flow through each boiler. But if one boiler fails, all flow could go through one and I like to use that pressure for pump sizing.
How do I force the critical path to include the boiler when both are connected? I'll have 2 pumps in parallel and suspect will have the same issue there. One dirty workaround would be to not actually connect the pipe of the second boiler. I use R2023 and wasn't able to use the hydraulic separation.
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec