Pipe Fittings: routing preference

Anonymous
Not applicable

 

Hi all, I need your help for the following reason: 

in the current project I need to model the FS system and specifically for the reducing tee I have 2 different types:

 

A. Mechanical bolted branch

B. Grooved tee

 

the type A connects 100/150 mm pipes to 15/50 mm branch pipe

The type B connects 100/150 mm pipes to 65+ mm branch pipeCapture.JPG

I  have attached the routing preference.

 

The question is how can I set it in order to model the 2 fittings automatically, because in this case Revit uses only one type, the first it finds. I tried also to modify the 2 families, leaving on the lookup table the diameters I want but Revit create a Custom fitting. 

 

Thanks 

 

Manu

Accepted solutions (4)
3,932 Views
10 Replies
Replies (10)
Message 2 of 11

Jacob_United
Advocate
Advocate

Interesting problem you've got there, I can think of a couple of things I would likely attempt. But most them are pretty rubbish.

 

If you could upload the two families I could definitely have a look at it for you.

 

If my post answers your question, please click... Just kidding!
0 Likes
Message 3 of 11

Anonymous
Not applicable

Hi Luke,

 

thanks for your messagge. I have attached the 2 families. They are the "original" version as I received, I mean before starting my modification (that seems useless anyway).

 

Thanks again

0 Likes
Message 4 of 11

robert.klempau
Advisor
Advisor
Accepted solution

Hello Manu,

 

What I see in your picture is that your Min Size and Max Sizes are not correct.

 

Revit wil look at the frist line of the junctions then the second line, etc.

So your first family A must be at the first row and the Min Size = 15 and the Max Size = 50

the second row is family B and the Min Size = 65 and the Max Size = max size of your pipe segment.

 

Note: Your families must have the correct data for the different sizes that can be placed or generated by Revit when using the Trim / Extend function.

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

0 Likes
Message 5 of 11

Anonymous
Not applicable

Hi Robert,

Thanks for your reply. The point is that for the first row 15-50 mm is another fitting. My problem is for the 2nd and 3rd row. In particular the tee A will connect pipe 150 mm with a 15 - 32 - 40 - 50 mm and tee B will connect pipe 150 mm with 65 - 80 mm.

So the reason why you can find the second at the third row of the routing preference set in that way.

Hope I am more clear now and thanks again for your  message 🙂

0 Likes
Message 6 of 11

robert.klempau
Advisor
Advisor
Accepted solution

Hello @Anonymous,

 

is this what you want to achieve?

 

routing pref pipes.png

 

see attachment for 2016 example project.

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

0 Likes
Message 7 of 11

Anonymous
Not applicable

Capture.JPG

Not exactly. I would like to do something like this above, but allowing me to do automatically instead of changing the routing preferences everytime I need to switch from one tipe to another or select the family and change it.

Thanks for your time!

0 Likes
Message 8 of 11

robert.klempau
Advisor
Advisor
Accepted solution

Hello @Anonymous,

 

Aha, Smiley Happy Now I understand.

Sorry for that.

 

Unfortunately, that is not possible in one Pipe Type.

But there is a workaround / solution.

 

You need two Pipe Types.

 

1: with the "S_Victaulic-IPS-Mechanical-T Outlet Style 920-920N: Standard" as your junction family

2: with the "FS_Victaulic-FP-Tee No 1: Standard" as your junction family

 

two Pipe Types.png

 

So in the main Pipe and takeoff pipes larger then 50 you need the "Standard Takeoff large 65+" Pipe Type with the "FS_Victaulic-FP-Tee No 1: Standard" family.

For the small takeoff pipes you need the "Standard Takeoff large 65+" Pipe Type with the "S_Victaulic-IPS-Mechanical-T Outlet Style 920-920N: Standard" family.

 

Then it works.

diferent pipe types.png

 

I attached the Revit 2017 Example.

Please have a look at it and let me know it this works for you.

 

 

 

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

Message 9 of 11

Anonymous
Not applicable
Accepted solution

Hi Robert,

 

thanks a lot for your solution and time!

 

Regards,

 

Emanuele

0 Likes
Message 10 of 11

robert.klempau
Advisor
Advisor

Hello Emanuele,

 

No thanks, I like to help Smiley Happy

 

You're more than welcome to ask more questions.

That's why the Forum is there.

 

If my post solved your problem, could you be so kind and share that with others by accepting that as a solution?

 

Thanks,

 

Kind regards,

 

Robert Klempau

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

0 Likes
Message 11 of 11

robert.klempau
Advisor
Advisor

Hello @Anonymous,

 

Great that it solved your problem.

Just a small question.

To help others too, would you be so kind and accept post 8 of 10 as a solution so others can see that.

 

Thanks.

 

Robert

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

0 Likes