How to set Air Terminal with 2 connection?

How to set Air Terminal with 2 connection?

marco.defina
Collaborator Collaborator
3,529 Views
24 Replies
Message 1 of 25

How to set Air Terminal with 2 connection?

marco.defina
Collaborator
Collaborator

Hello,

 

i have the situation in the images below...I need to have 2 connection on a single air terminal. I setted on one the right information of classification and direction. The second connection only fitting connected at the first...

But when i want to have the pressure lost or i check the ducts systems i receive error...Wrong direction fluid...

 

 

1.JPG2.JPG

 

 

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Accepted solutions (3)
3,530 Views
24 Replies
Replies (24)
Message 2 of 25

robert.klempau
Advisor
Advisor

Hello @marco.defina,

 

Can you upload the Air Terminal family?

your screenshots are not in English so that's a bit difficult for us. 🙂 

 

I saw in your picture that you linked the connectors.

is that correct? 

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

0 Likes
Message 3 of 25

marco.defina
Collaborator
Collaborator

Attached...

 

Yes i linked the connectors, if i delete the connection change nothing...

 

 

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 4 of 25

robert.klempau
Advisor
Advisor

Hello @marco.defina,

 

As far as i know you can’t link a preset connector to a fitting connector. It will generate errors in Revit.

A fitting connector is only used in fitting families.

 

I do not understand why you would use this method.

Why don’t you add another supply Air connector to the other side.

You could divide the Air Flow over the two connectors if you like.

to understand how connectors work, please see the pdf from Martin Schmid: Getting into the Flow: Understanding Connectors in Revit. MEP Content.

If my post answers your question, please click the "Accept as Solution" button. This helps everyone find answers more quickly!

Kind regards,
Robert Klempau
Senior Consultant AEC
Cadac Group AEC BV

Message 5 of 25

marco.defina
Collaborator
Collaborator

Thanks for the info!

I setted the two connectors with flow half and half...But i have the same issue...

 

Some equipment is wrong, Revit says that i need to have all the equipment with global, calculated and the two connectors must be connected...It's so!

 

I don't understand why doesn't work.

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 6 of 25

marco.defina
Collaborator
Collaborator

And with half flow my label indicate half flow on the drawing...So doesn't work fine...

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 7 of 25

marco.defina
Collaborator
Collaborator

I attached a piece of the project. If some can understand what is wrong...

 

Thanks

 

 

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 8 of 25

Anonymous
Not applicable

Hi Marco

 

You can try this.


Create a new instance parameter to the family which could be named e.g. "Connector flow". Then set a formula to the parameter "= Flow/2" (or Flusso/2 in your case).

 

Then set the flow configuration of both connectors in the family as "Preset" and associate the parameter "Connector flow" to the "Flow" parameter of the connectors under the "Mechanical flow".

 

When you then set the flow (Flusso) parameter of the air terminal to some value, the flow is automatically divided evenly to both ducts. I don't know if this has some side effects, but in my opinion this seems to work correctly

 

Two duct connections.png

0 Likes
Message 9 of 25

marco.defina
Collaborator
Collaborator

@Anonymous wrote:

Hi Marco

 

You can try this.


Create a new instance parameter to the family which could be named e.g. "Connector flow". Then set a formula to the parameter "= Flow/2" (or Flusso/2 in your case).

 

Then set the flow configuration of both connectors in the family as "Preset" and associate the parameter "Connector flow" to the "Flow" parameter of the connectors under the "Mechanical flow".

 

When you then set the flow (Flusso) parameter of the air terminal to some value, the flow is automatically divided evenly to both ducts. I don't know if this has some side effects, but in my opinion this seems to work correctly

 

 


Yes the side effect is what i write up...The label of air terminal give half of the flow Smiley Sad

 

I tried this solution but error on system remain, have you seen the test file attached?

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 10 of 25

SebasP_2188
Contributor
Contributor

i have same issue. the label of air terminal use flow in primary connector... that sucks

0 Likes
Message 11 of 25

ceyhunyuzuak
Advocate
Advocate

@marco.defina @SebasP_2188 

you can always use shared parameter to show your correct flow values in your labels but personally I don't use and I don't suggest people to use multiple connector element on an air terminal as it destroys your duct system and make it impossible (at least I couldn't find any way) to have Revit generate pressure loss report. instead, try to use 2 instances of air terminals in a spot and, I don't know, place them side by side so they look like one unit 🙂

0 Likes
Message 12 of 25

ToanDN
Consultant
Consultant

Do air terminals with more than one connector even exist?

0 Likes
Message 13 of 25

marco.defina
Collaborator
Collaborator

yes, in linear diffuser is frequently...

 

ldb_12_8-bild_1.jpg

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 14 of 25

ToanDN
Consultant
Consultant

@marco.defina wrote:

yes, in linear diffuser is frequently...

 

ldb_12_8-bild_1.jpg


And what model is it, and from what manufacturer?  I ask because I have linear diffusers all over my projects and not yet seen my HVAC consultants showing this type of plenum.

0 Likes
Message 15 of 25

ceyhunyuzuak
Advocate
Advocate

I don't know what brand his picture was from but TROX does it for slot diffusers.

For some manufacturers you can also have multi connection plenumbox for square diffusers and even have them split the plenum box inside with steel sheets. 

0 Likes
Message 16 of 25

marco.defina
Collaborator
Collaborator

the example of my screenshot is LTG, but the same you can find in trox VSD

 

Cattura.JPG

 

or Lindab

 

Cattura 2.JPG

 

and many more...

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.

0 Likes
Message 17 of 25

RobDraw
Mentor
Mentor
Accepted solution

A simple solution is to get families from the manufacturers.

 

 

 

I've solved this by using a single connector on the air terminal and connecting that to a plenum with multiple connectors.


Rob

Drafting is a breeze and Revit doesn't always work the way you think it should.
0 Likes
Message 18 of 25

SebasP_2188
Contributor
Contributor

@ceyhunyuzuak 
Thank you. there are several disadvantages to using shared parameter instead of native parameter. 90% of the air terminal families use the native parameter. managing 2 types of tags for the air terminal is counterproductive. In addition, reviewing all the other families of air terminal to use a shared parameter is not reasonable.

Thank you for your help. as I thought there is no real way to make it all efficient natively

0 Likes
Message 19 of 25

ceyhunyuzuak
Advocate
Advocate

That's the very reason I use my own shared parameters for everything I use. Airflow pressure drop, nominal sizes etc. for air terminals or other shared parameters for other types of components. When I need to download new family, I simply spend my 2 minutes to implement my shared parameters. So far, in my honest and humble opinion, it worths a lot. 

Message 20 of 25

marco.defina
Collaborator
Collaborator
Accepted solution

In 2017 i request support from Autodesk:

https://knowledge.autodesk.com/support/revit-products/troubleshooting/caas/sfdcarticles/sfdcarticles...

After 4 years the problem is still there. To resolve I split in 2 part the Air Terminal.

For the tag of air terminal i use a second parameter for splitted flow.

BIM Manager - HVAC and Plumbing designer https://www.autodesk.it/content/dam/autodesk/www/products/responsive-imagery/responsive-badges-compare/2019/navisworks-manage-2019-badge-75x75.pngApp AutoCAD per dispositivi mobili premiumNavisWorks Simulate3ds Max___________________________________________________________________________
Please use Mark Solutions!.Accept as Solution and Give Kudos!Give Kudos as appropriate to further enhance these forums.