You asked: "- Do you trust Revit heating and cooling calculations?". Answer — No, I don't and that's why.
The answer to this question lies in the method of calculation of the coefficient of heat transfer resistance (R).
(Here I translate my message from the Russian-language forum)
As you know, heat resistance Ro = Rin + R + Rout where:
Ro — heat resistance [m2 * K / W].
Rin — resistance heat absorption (inner wall surface ) is about 0.13 [m2 * K / W].
Rout — heat transfer resistance ( the outer surface of the wall) is about 0.04 [m2 * K / W].
R — thermal resistance of the wall.
Thus calculated heat transfer coefficient (call him as in Revit, the letter "U"), ie U = 1/Ro.
So, it seems that Revit simply ignores the value Rin + Rout and calculate heat loss (heat gain calculation has not yet been tested) only based on the value of the thermal resistance of the wall, ie R.
For example, a wall consisting of concrete, 200 mm thick, the thermal conductivity K = 1.04 [ W/m2 * K] (the value of 1.04 is taken as an example , although it is stated in the thermal properties of the material for concrete default).
Create a wall in Revit with these characteristics and we've got this:
Thermal resistance R = 0.1923 [ m2 * K / W].
Heat transfer coefficient (U) = 5.200 [ W/m2 * K] and calculated as 1/R.
Here is a screen of what happened:

Like until all true ...
Now, to verify the calculations let's create a space 10 by 10 meters with floor and roof. And let's take concrete wall 200 mm, which had just been created. The internal temperature of 5C degrees. Outdoor temperature -19C.
Doing Revit analysis of heat gain and heat load and the output is this:

Naturally assume that everything is OK. But the first check in any other program such as Rehau RAUWIN or calculation in just Excel will show that Revit ignores the value Rin and Rout.
Now show the results of calculations in the program, which is used for a long time — Rehau RAUWIN. Here again, the screen, which shows the composition of the wall and the coefficients Rin and Rout. Their values are sometimes other, here are the average:

Here it is seen that the value of heat transfer coefficient K (or "U" in Revit) eventually equals 2.96 [ W/m2 * K], which is much lower than in Revit! It happens because of proper accounting coefficients Rout and Rin. If we'll set them to the zero value in Rehau RAUWIN, we get the following result:

Which corresponds to the WRONG value of the coefficient, which we got in Revit, which once again proves that these factors Rin and Rout in Revit are excluded. And we got no form to set them right in Revit!
If we'll set in Rehau RAUWIN program a similar space, which is already calculated in Revit, we obtain the following values:

From this it is clear that a significant difference in the calculations.
What may be possible to solve this problem? Is there anything in Revit ability to specify these factors in the settings ? Is it true I described the problem and whether it exists at all?
(end of translation from forum). Original text in russian here.
By the way, a little later I found a way to set these coefficients fraudulently. Then all the calculations are correct. But if this will be interesting, will talk about later.
Cheers!