@ajay_johnganesan wrote:
Thanks for your valuable reply
I still have some doubts that I would like to ask. Lets say a Water tank (plumbing equipment) is set to Calculated & flow direction is Out connected to a fixture which is also set to Calculated. when both of this is set to calculated what would happen? Will calculation happens? i tried with a tank and connected to a washbasin where both are set to calculated but no calculation happens
Set the connect at the tank to Calculated.
Set the connections at plumbing fixtures to Preset or Fixture Unit and apply values for each fixture.
The flow values from each plumbing fixture will be passed through the pipe system, added together at each branch and the total flow will be applied (Calculated) at the water tank.
Preset means that you apply a fixed value for flow.
Fixture Unit applies diversity factors in accordance with US based "International Plumbing Code"
Calculated means that Revit calculates the value as I describe above.
System is similar to Calculated but is usually used when you have multiple equipment elements such two tanks in parallel (then you a apply a system factor to each to tell Revit what proportion of the Calculated flow will be apportioned to each piece of equipment).
It is all explained in that link that @RLY_15 shared.