google translator:
"I am trying to get the correct values of electric current per phase.
Basic settings:
Distribution System: 3 phases 4 wires 127 / 220V
Electric panel unbalanced, 3 poles; Voltage 220V; one column (custom panel table)
Revit 2019.
Circuits:
3 x 220V 5500W Showers
Current calculations (if performed correctly)
i = 5500/220 = 25A, the current is shared in two phases. as it is about three circuits, in a balanced situation we would have:
Corresponding phase 1: 25x2 = 50A
Current F2 = 50A
Current F3 = 50A
REVIT calculates the current per individual circuit perfectly, but it totally misses, changing the calculation method inexplicably, does anyone know a way around this problem? am I doing any incorrect settings?