Hi Revit MEP community
I am creating an air flow schematic layout in Revit 2016 and have all 3 floors of ductwork showing correct values however just 1 extract fan I am using is coming out with no airflow at all even though the connections and values have been set up correctly.
The system comprises of 6 return air valves connected to a fan which extract to the roof
The settings are as follows:
Air Valves
RETURN AIR
PRESET
OUT
FAN CONNECTION 1 (FROM AIR VALVES)
RETURN AIR
CALCULATED
IN
PARAMETER ADDED TO AIR FLOW 'CALLED FLOW'
FAN CONNECTION 2 (FROM AIR VALVES)
RETURN AIR
PRESET
OUT
FLOW PARAMETER ADDED TO AIR FLOW
Any ideas would be appreciated as this is becoming very irritating. (I have attached a partial screen shot showing problem)
Thanks in advance
Solved! Go to Solution.
Solved by ja1357. Go to Solution.
Solved by Skelly_PLAISANCE. Go to Solution.
Hi ja1357,
Modify the mechanical parameters of your two onnector element, in bidirectional and global
Skelly
I tried your suggestion and it worked thanks very much.
I don't understand why this is the case but it definitely works